Why is copper a better conductor of electricity than
aluminium?
Answers were Sorted based on User's Feedback
Answer / therion
Because copper has more free electrons than aluminium but
not as much as gold or silver.
| Is This Answer Correct ? | 6 Yes | 1 No |
since copper has high current carrying capacity..
it has low resistance..
it is of smaller in size then aluminium...
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / arul
The electrical capacity of any type of cables/wires are
depending on the heat withstand capacity of the material
wich can be calculated with the product of square of
current, Resistance of the material and Total time for flow
of current. I2RT. Resistance again can be calculated as
R=rho*L/A where rho is the resistivity, L is the length and
A is the area of cross section. So for a fixed current flow
and fixed Length of wire the area of cross section of the
cable is directly propotional to the resistivity.
resistivity of copper is 1.68x10 power -8 and that of Pure
Aluminum is 2.82x10 power -8. So.. for a specific current
flow, an aluminum cable size shall be 1.7 times that of
copper cable. This also is not recommented as the Aluminum
resistivity varries with the alloys and even with casting.
2.5 times the size of copper can be recommented for
Aluminum cables. Also as the temporature expansion of
Aluminum is 3 times that of copper. So all the termination
and joining areas shall be treated more sensible that of
copper.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / kevin fowke
Copper has a lower resistance than aluminium so for the
same cross sectional area a copper cable will have less
power loss.
| Is This Answer Correct ? | 2 Yes | 6 No |
What is the exact formula for one weber of magnetic flux?
How to calculate rated currennt Of Mcb for 2hp motor...
What is transient response?
How phase to phase voltage comes 440V.
i am in need of AC SYNCHRONUS MOTOR 30KW. ANY ONE KNOWS THE MANUFACTURER OF SAME. ALSO MOSFET AC CONVERTER 20KVA CONT.OUTPUT.
How can we step up ac and dc ?
What is 100% protection of generator? Why 100% is not used but 95% is generally used?
what is the contact resistance of vacume circuit breaker??
how to prepare the technical test
what formula can be apply to calculate the No of rtrand of a cable. ?
What is the difference between Earthing & grounding
I would like to know that the fault curretn at base load and at 10% generation will be same? Fault level of BUS remain same with different generation?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)