Answer / siddikh
1.polarity must be same
2.phase sequence must be same
3.turns transformation ratio must be sane
4.frequency must be same
5.% Impedence must be same
6.Vector group should be identical
| Is This Answer Correct ? | 19 Yes | 1 No |
Answer / irfan
1.polarity must be same
2.phase sequence must be same
3.equal voltage
| Is This Answer Correct ? | 11 Yes | 6 No |
1.polarity must be same ( Must be full fill )
2.phase sequence must be same (Must be full fill )
3.turns transformation ratio must be sane ( Desired )
4.frequency must be same ( Must be full Fill )
5.% Impedence must be same ( Desired as to ensure equall
load sharing of both the transformer
6.Vector group should be identical ( Desired )
| Is This Answer Correct ? | 6 Yes | 1 No |
following
1- KVA rating should be same
2- Voltage should be same and
3- frequency should be same
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / manoj tyagi
1. same voltage ratio
2. the per unit leakage impedence of the xer r based on
their own kva rating must be equal
3. ratio of eqv. leakage reactance to eqv. resitance should
be same for all the xers
4.transformer must be connected properly
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / ashok
1)polarity will be same.
2)phase sequence must be same.
3) turns ratio will be same.
4)impedance will be same.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vilas
1)Transformer primery voltage rating should be same.
2)phase sequence should be same .
3)polarity should be same.
4) Vector group should be same ,for example :dy11 etc.
These point to be considered while making parallel
operation of the tansformer.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / maneswar
1.polarity must be same
2.phase sequence must be same
3.turns transformation ratio must be sane
4.frequency must be same
| Is This Answer Correct ? | 3 Yes | 6 No |
Answer / khalander mulla
to manage load at integrated steel plant to recover plant
load
| Is This Answer Correct ? | 0 Yes | 4 No |
what is the setting of locked rotor in HT motor ? (answer expecting in percentage)
Is a induction motor rotate by back emf ? If not , then how it is rotate ?
What will happen if an AC induction motor is applied with DC voltage?????????Kindly give all the posssible answers...
How to calculate the current carrying capacity of sized cables, and there is any formula. please send to 'than.achu@yahoo.com'
how generater works
How we can convert H.P into KW or Vice versa
enlist types of dc generator
In case of 3Phase Supply, Voltage R-Earth/Neutral - 220 Y-Earth/Neutral - 220 Z-Earth/Neutral - 220 Total is -> 660Volts Then Why it is said that 3Phase supply is 440
6 Answers Hindustan Unilever Limited,
What are the advantages of star-delta starter with induction motor?
7 Answers Merchant Navy, Naval Academy, Samundra Institute of Maritime Studies, YMCA,
A 230V dc shunt wound motor has an armature resistance of 0,15Ω.When operating on no load at 650 rev/min the armature current is 6A . The motor takes a full load current of 85A. Calculate the full load speed if the field flux is (i) maintained constant (ii)reduced by 0,03
What is mean by CT Saturate? how do we calculate?
WHY TRANSFORMERS ARE RATED IN 11KV 22KV 33KV Instead off 10kv 20kv 30kv
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)