Answer / siddikh

1.polarity must be same
2.phase sequence must be same
3.turns transformation ratio must be sane
4.frequency must be same
5.% Impedence must be same
6.Vector group should be identical

Is This Answer Correct ?    19 Yes 1 No

parallel operation for tansformer which condition fill fil for that..

Answer / irfan

1.polarity must be same
2.phase sequence must be same
3.equal voltage

Is This Answer Correct ?    11 Yes 6 No

parallel operation for tansformer which condition fill fil for that..

Answer / virendra

1.polarity must be same ( Must be full fill )
2.phase sequence must be same (Must be full fill )
3.turns transformation ratio must be sane ( Desired )
4.frequency must be same ( Must be full Fill )
5.% Impedence must be same ( Desired as to ensure equall
load sharing of both the transformer
6.Vector group should be identical ( Desired )

Is This Answer Correct ?    6 Yes 1 No

parallel operation for tansformer which condition fill fil for that..

Answer / sanjayjssate

following
1- KVA rating should be same
2- Voltage should be same and
3- frequency should be same

Is This Answer Correct ?    0 Yes 0 No

parallel operation for tansformer which condition fill fil for that..

Answer / manoj tyagi

1. same voltage ratio
2. the per unit leakage impedence of the xer r based on
their own kva rating must be equal
3. ratio of eqv. leakage reactance to eqv. resitance should
be same for all the xers
4.transformer must be connected properly

Is This Answer Correct ?    2 Yes 3 No

parallel operation for tansformer which condition fill fil for that..

Answer / ashok

1)polarity will be same.
2)phase sequence must be same.
3) turns ratio will be same.
4)impedance will be same.

Is This Answer Correct ?    0 Yes 1 No

parallel operation for tansformer which condition fill fil for that..

Answer / dg mobh

1.polarity must be same
2.phase sequence must be same
3.turns transformation ratio must be sane
4.frequency must be same
5.% Impedence must be same load sharing of both the
transformer
6.Vector group should be identical

Is This Answer Correct ?    0 Yes 1 No

parallel operation for tansformer which condition fill fil for that..

Answer / vilas

1)Transformer primery voltage rating should be same.
2)phase sequence should be same .
3)polarity should be same.
4) Vector group should be same ,for example :dy11 etc.
These point to be considered while making parallel
operation of the tansformer.

Is This Answer Correct ?    0 Yes 2 No

parallel operation for tansformer which condition fill fil for that..

Answer / maneswar

1.polarity must be same
2.phase sequence must be same
3.turns transformation ratio must be sane
4.frequency must be same

Is This Answer Correct ?    3 Yes 6 No

parallel operation for tansformer which condition fill fil for that..

Answer / khalander mulla

to manage load at integrated steel plant to recover plant
load

Is This Answer Correct ?    0 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

What is the difference between resistance grounding system and resistance earthing system?

0 Answers  


What are the types of windings present in the ceiling fan? What winding will be effective first when we started the fan?What are the resistance and inductance ratios comparatively at the initial speed and full speed of the fan?

0 Answers   MIT,


A ii kv 1200 A Breaker combination fixed in a cubicle. How many ampere Fuse is required? If fuse is not using, Why?

0 Answers  


when transformer oil should be filtered/tested?

3 Answers  


why we use 11 kv 22 kv and so on ?

1 Answers   Air Force,






What is electrical earthing?

1 Answers  


Which element has power dissipated in it when the source is removed ?

2 Answers   SSC,


how can we choose the size of road crossing pipe for power cables

2 Answers   DLF,


When lag/lead/lag-lead compensation is employed?

0 Answers  


in three phase with neutral connection, what will happen,if the neutral is in open condition with single phase distribution panel

4 Answers  


Why the core in the distribution transformer is in even number

1 Answers  


For a DY11 lighting Transformer on primary side whee to connect fourth lead? from nuetral or from ground?

3 Answers   Sabic,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)