why are using bus ducts ? why not using cables

Answers were Sorted based on User's Feedback



why are using bus ducts ? why not using cables..

Answer / anand kumar shukla

as we know very well .we are use the busbar in busduct
because the current bearing rating of busbar is too much
high in compare to the cable.
we use the 150 x12 mm
150 x10 etc.
so the busbar mechanical strenth is too much strong than
cable. and busduct life is too long in compare to cable.

Is This Answer Correct ?    65 Yes 9 No

why are using bus ducts ? why not using cables..

Answer / kk_london

Normally busducts are used in between secondary side of the
transformer to panel where the distance will be short and
current carrying capacity will be high the busbars used are
generally of greater cross sectional area than the cables,
and also once they are fixed it hardly requires any
maintenance except for tightness in cables you need to do
period check of IR.

Is This Answer Correct ?    47 Yes 2 No

why are using bus ducts ? why not using cables..

Answer / srinu

Normally we wlli use this BUSDUCTS in LV side of the
transformer BcoZ the Current flowing in the LV side is more
than the HV side.

If we use cable we need Large Sq .mm for which cost is more
than to replace a cable. so, it is used. and another thing
is it has high mechanical strength.

Is This Answer Correct ?    23 Yes 4 No

why are using bus ducts ? why not using cables..

Answer / anand

The great advantage of Busduct are compact ( Sandwich type) and easy terminations at trf & panels. When we go for the high rise building with 20 floor, busducts ( one circuit)with floor tapping work out cheaper with less space and reduced distribution boxes. If cables to be laid then 20 circuits to be travelled from Ground floor.

Also busducts are very useful in industrial floor distibutions in a very economical way with more number of tapping.

Is This Answer Correct ?    14 Yes 0 No

why are using bus ducts ? why not using cables..

Answer / chirag mistry

Busbar SC level is high in comperision of cable.

Is This Answer Correct ?    8 Yes 1 No

why are using bus ducts ? why not using cables..

Answer / m.sridhar

above 1000 Amps ,busbar is mandatory as per IE rules,as there is no protection between transformer secondary and it breaker,probability of busbar failure is very less compared to cable.

Is This Answer Correct ?    4 Yes 0 No

why are using bus ducts ? why not using cables..

Answer / lekha

On LT side, we can use insulated bus bars insted of cables.
Advantage is that we can take tap from busbar at many
places. Such bus bars of Schnieder, L&T are available in
market.

Is This Answer Correct ?    7 Yes 4 No

why are using bus ducts ? why not using cables..

Answer / neet

Normally busducts are used in between secondary side of the
transformer to panel where the distance will be short and
current carrying capacity will be high the busbars used are
generally of greater cross sectional area than the cables,
and also once they are fixed it hardly requires any
maintenance except for tightness in cables you need to do
period check of IR

Is This Answer Correct ?    1 Yes 0 No

why are using bus ducts ? why not using cables..

Answer / sachin gopi

The transformer rating is more than 1000 KVA,Then current rating will be high so cables should not used.by using bus ducts

Is This Answer Correct ?    0 Yes 0 No

why are using bus ducts ? why not using cables..

Answer / muhammad irfan ali

Bus Way Good as Compare to cable ,because it has high current rating
and you take supply different location
but it is not good for Medium voltage because it has no high current and also cost is higher then cable

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

in telecom we are using neutral?

1 Answers  


What is meaning of DRU in gen.of AVR.

2 Answers  


Explain different types of d.c motors? Give their applications

0 Answers  


Single line digram for 11 kV to distribution use go,la and do

0 Answers   SK,


what is the difference between earth and neutral.

9 Answers   DLF,






how we can calculate cable size for any load & any type of cable material ?

1 Answers  


what will happen if dc supply is given to ac motor?

9 Answers   CTS,


how to commissioning the genset with amf panel?

0 Answers   Cummins,


What is the kva?

2 Answers   Makino Auto, SAL Steel Power, Sapphire Group,


why do transformer make a sound

4 Answers  


What is meant by RCCB

3 Answers  


What is a roll of adopter panel in terms of h.t. Panel ???

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)