Answer / ranjan prasad
Normally NGR is being connected with the neutral of
transformers or Generators to limit the the fault current.
This NGR basically gives the out put in terms of voltage
during the fault condition (like Earth Fault). To sens the
voltage during fault condition, isolation transformer is
connected across NGR for voltage feed back. This v f/b goes
to the relay to operate in case of earth fault depending
upon the setting done at relay.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / aamod tripathi
NEUTRAL GROUND RESISTANCE RELAY IS A RELAY WHICH WILL
OPERATE UNDER AN EARTH FAULT. AND WILL GET ACTIVATED IN
CASE OF AN EARTH FAULT ONLY TO ACTIVATE THE BREAKER IN
ORDER TO TRIP THE CIRCUIT.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / biswajit sahoo
THIS IS BASICALLY REF TYPE RELAY. iT WORKS ON PRINCIPLE OF
DIFFERENCE IN NEUTRAL CURRENT IE TRANSFORMER END AND
CONSUMER FEEDER END
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / angela tong
NGR is neutral ground resistance which is inserted between
neutral and ground to operate during ground fault happens.
It could prevent generator or transformer from overvoltage
or arc flash grounding transient overvoltage and clear the
fault up.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is required of exietation to the alternater.
why using transformer and thyristor switch in 3 phase apfc panel
How can we parallel two transformer with vector gorup YNd11 and YNd1?How is connection two transformer GT?
what is the capacitance of a single conductor
Which type of Oil is used in transformers, & what is its strength?
CAn a TJM 10 relay measure over current ?
the current which flows during lightening is ac or dc,,,,,,,,,,, WHY
Which rccb 30ma,100ma,300ma sensitivity should be used in domestic line and what is difference, advantage and disadvantage of all three
which is batter in construction job,ELCB or RCCB?
Why motor initial starting current is high?
i am going to give the JSEB,RANCHI exam for power plant,so i need some samples of papers related to that,so please send me these papers by my mail id.
WE know that for Inductor X=2pifL,In DC f=0,then X=0 so,V=IX=0;But In the DC excitation of rotor of AC generator,DC motor field coil which coils are inductor so why does not applying DC voltage short the rotor coil of AC generator and field coil of motor?If it would then DC source might be damaged but it is not happened. Why does the strand conductor of Electrical power transmission line make twist?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)