How to calculate % Impedence?
Answers were Sorted based on User's Feedback
Answer / salahudeen
itis the ratio of for a given supply voltage the full load
current flowing though the secondary wdg when secondary is
short circuited.
EXAMPLE Given 100v the current is 5 A then 100/5=20
then pERcent=0.02
why this value?
it ios a crucial factor determining the current carrying
capacity of the protection/switch gear of the transformer
N/w
ie suppose rated current is 7 A then switvh gear capacity
=7+0.02(7)=7.15 A
Is This Answer Correct ? | 3 Yes | 0 No |
IT IS THE RATIO OF THE VOLTAGE DROP IN AN IMPEDANCE WHEN
FULL LOAD CURRENT IS FLOWING IN IT TO THE BASE VOLTAGE OF
THE SYSTEM.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / somnath sharma
I think there is no difference in percentage impedance and p.u impedance except the basic one that is % impedance in calculated in per 100 while the p.u is calculated in per unit.
So if u simply multiply the value of p.u impedance with the 100, u will % impedance. I hope u must be knowing how to calculate p.u.
Is This Answer Correct ? | 4 Yes | 3 No |
What is the phase relationship between the primary and secondary voltages of a transformer?
i want to know about for what reason we are using star delta starter? how it works? what are the advantages?
I am using submission of two ct in one and half scheme for 67/67N protection. Both CTs star point is grounded separately near ct box.Will two point ground give wrong tripping to 67/67N during fault or no matter.
What is flow meter?
what is reactive power?
What types of question are done for diploma students in aptitude test
in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 33v to 430.v.
is there any current and voltage drop on liquid resistance starter water/soda tank ?
Whatis the current capacity of 33KV/ 0.433KV transformer on Primary and secondary side/
Why is our voltage always seems to be 3.3Kv,11Kv,66Kvetc.. why not 40Kv,39Kv,65Kv???
why series motor cannot be started on no-load?
Testing procedure of DG alternator stability test