How can we calculate ngr resistance for a generator and
Transformer ?
What type of transformer requires ngr ?
Answers were Sorted based on User's Feedback
Answer / ramesh
NGR-Neutral Grounding Resistor.It is used to limit the
fault current in the neutral line.calculation based on fault
current in stator in generator and star side in trfr
| Is This Answer Correct ? | 25 Yes | 4 No |
Answer / ravi kumar purohit
DESIGN AND SELECTION CRITERIA OF
NGR
Neutral Grounding Resistor:
The power transformer secondary 6.6kV neutral shall be
medium resistance earthed in order to limit the 6.6kV
system earth faults to low values such as to limit
excessive damage to 6.6kV equipments.
Also that the earth faults are not too low value to cause
earth fault relay non-operation.
System voltage = 6.6kV
System voltage per phase = 6.6/√3
Vph = 3810.6Volts
Earth fault current (I) =50A for 5 sec
NGR calculation is done on the basis of following formula,
Vph= I X R
R= Vph / I
R= 3810.6/50
Resistance= 76.21 Ohms
NGR Selected is 6.6kV , 50A, 76.2Ohms, 5sec.
Normally 50 A
| Is This Answer Correct ? | 21 Yes | 3 No |
The value of the NGR to be inserted in the cicuit can be
calculated by the simple formula
R = V / (√3 * I)
Where V is the System Line voltage in Volts
I is the value of the fault current to be limited
In general practice the fault current is limited to the
full load rating of the largest equipment available in the
system.
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / madivalanagaraja@gmail.co
It is similar to the ground resistor calculation for transformer
The typical example was answered earlier for transformer dt.19-06-2009
Neutral of transformer can be grounded solidly earthed OR with Neutral Grounded with Resistance.
Typical shunt calculations fro 5 MAV 11/6.6 kv transformer neutral are as :_
Transformer rating = 5 MVA
Voltage ratio = 11/6.6 KV
Vector Group = Dyn11 (6.6 KV ground through Resistor)
During Earth fault voltage between Neutral
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / a s bhandari
Ohmic value of neutral grounding resister for a transformer is calculated as follows:
R = Vph/ I where I - value of fault current to be limited to flow through the neutral path, normally it is 50A for 5 sec.
Based on above, for 6.6 kv star side of a transformer
resister value shall be 76.21ohm.
| Is This Answer Correct ? | 0 Yes | 3 No |
What is meant by Floating Neutral? how to prent
What are all the conditions to protect generator & turbine in thermal power plant?
why +24 v and -48 v give to BTS? If -48v protect from surge then why we not use -24 v?
why we +ve load distribution in 24v and -ve load distribution in 48volt in the telecom sector.?
MCB MCCB ACB VCB
132/6.6ππ πππππππππππ πππππππ πππ πππ πππππ πππ πππππππππ. πΈ'ππ πππππππ πππππππππππ ππ 6.6ππ/415π πππ πΈ πππππππ πππππππ ππ ππππ πππππ πππ ππ ππ 13/6.ππ πππππππππππ?? πΈπ π½π.. ππππ π ππ’??
What is a roll of adopter panel in terms of h.t. Panel ???
Is there any relation between transformer capacity and its bdv?
why alternator is used instead of dc generator and induction generator
To attain a powerfactor more than .95, how much kvr should we use for 100 HP of current
4 Answers Bhel, Scooters India,
plzzzzzzzzz plzz send me the papers of JSPL WRITTEN TEST..SO that i can prepare for the test in electrical engg..
1 unit or 1 kwh means how much kva
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)