How can we calculate ngr resistance for a generator and
Transformer ?
What type of transformer requires ngr ?
Answers were Sorted based on User's Feedback
Answer / ramesh
NGR-Neutral Grounding Resistor.It is used to limit the
fault current in the neutral line.calculation based on fault
current in stator in generator and star side in trfr
Is This Answer Correct ? | 25 Yes | 4 No |
Answer / ravi kumar purohit
DESIGN AND SELECTION CRITERIA OF
NGR
Neutral Grounding Resistor:
The power transformer secondary 6.6kV neutral shall be
medium resistance earthed in order to limit the 6.6kV
system earth faults to low values such as to limit
excessive damage to 6.6kV equipments.
Also that the earth faults are not too low value to cause
earth fault relay non-operation.
System voltage = 6.6kV
System voltage per phase = 6.6/√3
Vph = 3810.6Volts
Earth fault current (I) =50A for 5 sec
NGR calculation is done on the basis of following formula,
Vph= I X R
R= Vph / I
R= 3810.6/50
Resistance= 76.21 Ohms
NGR Selected is 6.6kV , 50A, 76.2Ohms, 5sec.
Normally 50 A
Is This Answer Correct ? | 21 Yes | 3 No |
The value of the NGR to be inserted in the cicuit can be
calculated by the simple formula
R = V / (√3 * I)
Where V is the System Line voltage in Volts
I is the value of the fault current to be limited
In general practice the fault current is limited to the
full load rating of the largest equipment available in the
system.
Is This Answer Correct ? | 6 Yes | 5 No |
Answer / madivalanagaraja@gmail.co
It is similar to the ground resistor calculation for transformer
The typical example was answered earlier for transformer dt.19-06-2009
Neutral of transformer can be grounded solidly earthed OR with Neutral Grounded with Resistance.
Typical shunt calculations fro 5 MAV 11/6.6 kv transformer neutral are as :_
Transformer rating = 5 MVA
Voltage ratio = 11/6.6 KV
Vector Group = Dyn11 (6.6 KV ground through Resistor)
During Earth fault voltage between Neutral
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / a s bhandari
Ohmic value of neutral grounding resister for a transformer is calculated as follows:
R = Vph/ I where I - value of fault current to be limited to flow through the neutral path, normally it is 50A for 5 sec.
Based on above, for 6.6 kv star side of a transformer
resister value shall be 76.21ohm.
Is This Answer Correct ? | 0 Yes | 3 No |
how to calculate current carrying capacity in power cable?
what is the differencce inn series and cascade connection??
Necessity of transformer earthing
dg started in plc mode and load taken later one battery terminal connection will be disconnected by loose connection what will happen for dg and shall we connect battery terminals while dg in load time?
what is AB switch???
what is the method to calculate the voltage drop for number of meters Example 250volts I/p at one end if the cable length is 50 meters what could be the drop?, after 100 meters how much? needs formulae.
how to prepare the technical test
transformer is working or not with supply of DC?
Difference between split ac and cassete ac?
What is the maximum current carrying capacity for both copper and aluminium cables for 1sqmm?
Explain the operation principle, advantages and disadvantages of the following converters: a) A 12 pulse converter b) A Switch-mode inverter c) A thyristor inverter
Which transformer is suitable for 220/11 kV, 60 MVA, distribution , Y-Y or D-Y or Y-D, give comparison for the same.