Answer / ramesh

NGR-Neutral Grounding Resistor.It is used to limit the
fault current in the neutral line.calculation based on fault
current in stator in generator and star side in trfr

Is This Answer Correct ?    25 Yes 4 No

How can we calculate ngr resistance for a generator and Transformer ? What type of transformer requi..

Answer / ravi kumar purohit

DESIGN AND SELECTION CRITERIA OF
NGR

Neutral Grounding Resistor:

The power transformer secondary 6.6kV neutral shall be
medium resistance earthed in order to limit the 6.6kV
system earth faults to low values such as to limit
excessive damage to 6.6kV equipments.
Also that the earth faults are not too low value to cause
earth fault relay non-operation.

System voltage = 6.6kV
System voltage per phase = 6.6/√3
Vph = 3810.6Volts
Earth fault current (I) =50A for 5 sec

NGR calculation is done on the basis of following formula,

Vph= I X R

R= Vph / I

R= 3810.6/50

Resistance= 76.21 Ohms

NGR Selected is 6.6kV , 50A, 76.2Ohms, 5sec.

Normally 50 A

Is This Answer Correct ?    21 Yes 3 No

How can we calculate ngr resistance for a generator and Transformer ? What type of transformer requi..

Answer / pavan

The value of the NGR to be inserted in the cicuit can be
calculated by the simple formula

R = V / (√3 * I)

Where V is the System Line voltage in Volts
I is the value of the fault current to be limited

In general practice the fault current is limited to the
full load rating of the largest equipment available in the
system.

Is This Answer Correct ?    6 Yes 5 No

How can we calculate ngr resistance for a generator and Transformer ? What type of transformer requi..

Answer / madivalanagaraja@gmail.co

It is similar to the ground resistor calculation for transformer

The typical example was answered earlier for transformer dt.19-06-2009

Neutral of transformer can be grounded solidly earthed OR with Neutral Grounded with Resistance.

Typical shunt calculations fro 5 MAV 11/6.6 kv transformer neutral are as :_

Transformer rating = 5 MVA

Voltage ratio = 11/6.6 KV

Vector Group = Dyn11 (6.6 KV ground through Resistor)

During Earth fault voltage between Neutral

Is This Answer Correct ?    1 Yes 0 No

How can we calculate ngr resistance for a generator and Transformer ? What type of transformer requi..

Answer / a s bhandari

Ohmic value of neutral grounding resister for a transformer is calculated as follows:

R = Vph/ I where I - value of fault current to be limited to flow through the neutral path, normally it is 50A for 5 sec.

Based on above, for 6.6 kv star side of a transformer
resister value shall be 76.21ohm.

Is This Answer Correct ?    0 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

mostly the questions were from machines... d.c. machines, transformer, synchronous and induction all theory paper........ few from power system... but the level of paper was easy.....

0 Answers   IFFCO,


what is diffrence between neutral and earth wire

23 Answers   Bhel, Esab, MTNL,


What is the need for checking knee point voltage for CT's?

1 Answers  


How Arc Produced in Circuit Breaker When the contacts of the circuit breaker open.

1 Answers  


What power factor maintain you maintain at u r organisation

14 Answers   Wheels India,






Why alternators are rated in KVA?

12 Answers  


calculate multiplication factor of a trivector meter with line ct ratio 200/5A, line PT ratio 11000/110V and meter CT ratio 200/1A and meter pt Ratio 11000/110V.

4 Answers  


what is transient enclosure vltage , very fast transients, very fast transient over voltages

0 Answers  


i work as a technician at a private company.. i used to take amp reading for certain appliances such as air con.. the problem is when i clamp the neutral, wire there is a current reading.. from my understanding for single phase system neutral should not have current unless if the circuit is not complete.. yet the air con still work

3 Answers  


why core losses and copper losses does not depend on power factor?

5 Answers  


what is the difference between indoor package substation and outdoor

3 Answers  


what is the difference between cable routing and scheduling?

4 Answers   Techno Labs,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16637)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)