1) How to calculate battery backup for ups as well as solar
with complete formula elaborately......
Answers were Sorted based on User's Feedback
Answer / kuzhali
ups back up time=(AH rating*volt*power factor)/total load
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / velmurugan, so/d, barcf, kalpa
Consider the 2 KVA online UPS.
specifications are as follows: output voltage: 230V, Pf:
0.8, Load is 1600W. DC bus voltage is 96V.
Now Total output is = 2000 VA
PF of the load is = 0.8
There fore output in watts = 2000x0.8= 1600W.
Efficiency of the inverter is 80% therefore power input to
the inverter will be = 1600/0.8= 2000W
DC current of the inverter section= Watts / Voltage
Consider the fully charged voltage = 13.5X8=108V
The DC bus voltage
up to which the battery can deliver= 10.5x8=84 Volts.
therefore maximum current drawn by the inverter when battery
is in line = 2000/84=23.8A
Now consider the backup required for the load, i.e 1 hour
back up is required to safe shutdown loads when power supply
is not available.
Consider a class 10 type of battery where it has a
efficiency of 90%, 300Ah battery.
the effective AH available for the load is 300x0.9=270AH.
For 1 hour duration the discharge current will be 27.0A
which is higher than the required value of 23.5A.
There fore for 2 KVA online UPS having the load of 1600W
with 0.8 pf load, it requires 300AH of 8 nos of battery for
1 hour backup.
| Is This Answer Correct ? | 0 Yes | 2 No |
What is the maximum and minimum rating of UPS?
Which starter can be used for 3 phase verriable speed (2 stator wdg) induction motor ?
Explain the different regions in frequency response?
what is the requirement of commutator in a universal motor?
write a c++ code that receives an integer number and display the sum of the number and its revers integer?
We have a distribution transformer of 750KVA/11kv/440v and an AVR (Servo Stabilizer) of 750KVA on the LT side of distribution transformer. Also we have an ACB of 1200A on the output of distribution transformer (that is on the input of AVR). We want to have an MCCB on the output of AVR. What should be the rating?
what causes contact chatter when there is no demand on the air conditioning unit?
what is the IS foe lightning arrester?
what is the range of thermal overload and over current. Answer should be in percentage of current.
what are the types of Distribution transformer vector group please explain
what is mean by single phasing used for electrification in rural area of maharashtra ?
I'm generating a pulse of 3V with frequency 80Hz (12.5ms time period) and pulse duration 0.125ms and feeding it to a transformer since i want the pulse to get amplified around 60V. At the output amplification s happening but the pulse is changed to a spike, can you tell me what could be the reason? (an ordinary transformer 220V-12V stepdown transformer is reverse connected ie. now it is 12V-220V stepup and voltage amplification happens)
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)