explain why the secondary terminal of current transformer
should not be lift open circuited.
Answers were Sorted based on User's Feedback
Answer / ramesh kumar k
Mainly the current Transformer works on the principle that
Primary mmf = secondary mmf
i.e
Primary AmpereTurns(AT) = Secondary AT
so if the secondary is Open circuited, there is no current
in the Secondary hence secondary AT=0. In that case there
is no opposing mmf in the secondary to neutralize the
primary mmf. So the CT secondary will induce heavy
voltages and winding of the secondary will burn...
simply to understand guess what happends if we pump water
into a tank without opening valves for water to go out..
Is This Answer Correct ? | 11 Yes | 0 No |
Answer / gulshan goyal
the mmf developed in the primary side will depend only on
load current which is highdue to which there will be high
flux in secondary also hence if we open circuit the
secondary the current present in sec will be zero,a very
high voltage will be generated which cause hazard.
Is This Answer Correct ? | 3 Yes | 1 No |
How can we increase the capacity of exixting capacitor bank??????????????? PLS. Help
On Which Pressure PRV is operated.
why there using acb enclosure in big buildings
Supose we have one 220v A.C fan.if we provide 220v D.C what will be happen?
how we can find of current direction(supply comming/out going direction) when a transmission line passing through sides.
Why is the starting current high in dc motor?
what is the difference between 230v and 115v?
1 Answers Bhushan Power Steel,
How voltage regulation is calculated for over head transmission line? What do we mean by Conductor constant while calculating voltage regulation? how it is differ for for diffrent type of conductor say AAAC DOG & AAAC RACOON conductor?
what is bus PT ?
PIU how does work?
How can eliminate noise problem inside temperature controller temp. variation due to contactor chattering problem.
Dir sir we have 750 kva Caterpillar dg set we are fas on different problem we start dg set ofter 1 mint apply load around 500a dg was run one or 3 mint after 3 mints dg was shutdown automatic how to face tis problem