How check proper electrical earthing of machine.
Answers were Sorted based on User's Feedback
Answer / iamdon
Earthing of a machine is checked with the help of a devies
called earth tester.For proper earthing, reading of tester
should be from 4-10 ohms approximately.
Author:arbelectbit@yahoo.com
Is This Answer Correct ? | 16 Yes | 8 No |
Answer / k.cs
This method of checking is ok,but there is a chance of
electrical shock may be felt by testing person by mistake.
Hence it is always advisable to test at electrical socket
with out connecting machine in the socket, that is there
willbe a 1-3 voltages should be in between neutral and
earth points.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / puneet
earthing we can check by measuring the voltage betwwen phase and machine earth point if we get the voltage then it is ok
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / avi gulia
earthing can be checked by either checking voltage between the phase and earth or by checking voltage between the neutral and earth it should be 2 to 4 volts.
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / b soni
Earthing of a machine is checked with the help of a devies
called earth tester.For proper earthing, reading of tester
should be from 1-5 megaohms approximately.
Is This Answer Correct ? | 4 Yes | 12 No |
how to calculate current carring capacity of cable and cable selection? 1) copper flexible cable 2) copper armoured cable 3) Aluminium cable
Mechanism of Wye Delta Starter?
How can calculate the efficency of the rectifier. input 240V AC, current 5 amps,P.F 0.98, Output is 54 V DC,62.6 A.
if voltage is not builed up in small generator what will be the reason?
which is the best book of electrical objective for placement
How to check the cable fault / hv test of transformer cable.
In UPS, battery connections if parallel connection given, what will happen?
what effect will 10 milliampere current cause to human body
What is the difference b/w Earthing and Grounding?
how can found motors folt current ? how can disided circuit breakers caoicity and breaking capicity ?
if z transform lies in ROC then. a)system is stable b)inverse of system is stable c)both system and its inverse are stable.
what is the full name of ELCB &MDB <MCB