generally on the roadside v hav 11kv line which is being
step down to 440v line to line....so any1 can tell me which
type of transformer they r using whether it is star to
delta,delta to star etc...???
Answers were Sorted based on User's Feedback
Answer / indra bhushan kumar
high voltage side should be connected in delta ,while low
voltage side in star because in star connecton,a ground or
neutral can be fecilitated
| Is This Answer Correct ? | 31 Yes | 3 No |
Answer / kranthi
IT MUST BE DELTA STAR..i.e.,on the meter side they require
415/1.732 V voltage with neutral point
| Is This Answer Correct ? | 16 Yes | 5 No |
Answer / shahulsnfa
see in delta minmum potential difference is 440. but in
star 440 as well as 230 is available. focusing in consumer
side the distribution transformer will have delta in
primary and star in secondary.
| Is This Answer Correct ? | 13 Yes | 3 No |
The transformer is Delta - Star connected Transformer i.e.,
11kv is given to Delta connected side and 440v is given to
Star connected side of the transformer.
Delta side dont have neutral, while transmission neutral is
not needed.if neutral is used totally 4 wires have to be
used otherwise 3 wires are enough. 440v side we give to
homes, there a neutral is need so connected in star.
in Delta side line voltage = phase voltage. so 11kv voltage
is same.
homes need the voltage of 230v, in star the line voltage is
not equal to phase voltage. line voltage is 440v and phase
voltage is 230v.
so the transformer needed is Delta-Star
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / prithvi narayan sinha
While in Star connection we can reduce the line voltage by
57.7% due to the fact that we get the line voltage as 1/sqrt3
of the phase voltage ,hence reduction becomes easier and
convenient too. while in delta we get the line voltage=
phase voltage.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / rajkumar
11 kv side delta connection and 440 v side star connection
bcos delta have no nutral so no need to run 4 runs of cable
need only 3 runs. in 440 v side we need nutral so it
connected in star connection.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / arsenal
i think delta is used in the lv side bcoz in star
connection the voltage phase value will be greatly reduced
as such current is greatly increased so a large conductor
has to be used for transmission which increases the cost
and other losses.
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / sabale.dnyanehswar@gmail.com
generally it will be 1.1 kv/0.415kv step down star -delta
transformer.
| Is This Answer Correct ? | 3 Yes | 22 No |
how does the thyistor work in dc drive?
1) why a dg set shows variation of power factor and load when synchronised with other dgs? 2)Why the load sharing is not become equal in all dgs?. 3)When a dg set will not run on auto start?
IR value for 30kw lt motor
How delta connection in the primary of distribution transformer reduces harmonics?how delta connections reduces harmonics?Please answer me...Hope that question is correct.
why phase to phase voltage is 400v while phase to neutral is 220v?
in india ac frequency is 50hz, but in foreign countries it is 60hz,whwt is the reason
which type of motor is used in lift ?
Here iam a question with SYNCHRONIZATION PANNEL related issue, as i want to design a SYNC.pannel board iam giving the 2 nos of 1MVA Generators to sync pannel , then what wil be the out put of the sync pannel, whether it wil be one cable coems from the sync panel or two cables.. as iam using two transformers to meet my load demand, so pls clear me whether two cables comes from sync panel to connect to transformers or only one cable
for selection of transformer we will considering 5 to 6 times of starting current of higher rating motor connected to secondary side. according to process wise we will start the motors gradually suppose if we will start 15 to 20 motors at a time wat will happen?
WHY WE DO NOT TAKE THE POWER FACTOR MORE NEARER TO UNITY IN AC GENERATOR?
What are the different protection systems takes place on control panel board?
it is difficult to interrupt a capacitive current because (a)it has a leading power factor (b)current magnitude is very small (c)the restriking voltage can be high (d)stored energy in the capacitor is high
2 Answers DGVCL Dakshin Gujarat Vij Company, MGVCL, UGVCL Uttar Gujarat Vij Company Ltd,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)