HOW DOES THE PERCENTAGE DIFFERENTIAL PROTECTION WORK IN
POWER TRANSFORMER
Answer / raghavendran.r
In percentage differential relays, the current from each
current transformer flows through a restraint coil. The
purpose of the restraint coil is to prevent undesired relay
operation due to current transformer errors. The operating
coil current | i1 - i2 | required for tripping is a
percentage of the average current through the restraint
coils.
i1-i2 >=k(i1+i2)/2= k*iavg
where k is the proportion of the operating coil current to
the restraint coil current. For example if k = 0.1, the
operating coil current must be more than 10% of the average
restraint coil current in order for the relay to operate.
Is This Answer Correct ? | 4 Yes | 0 No |
Grid fault level [KA]?
What are the methods/types of distance protection schemes used in transmission system?
where we use 1 phase & 3 phase supply ?what is major advantage using 3 phase over than single phase ?
what is the difference between phase and neutral?
3 Answers IAF, Indian Airlines,
what are the differance between neutral and earthing?
How can eliminate noise problem inside temperature controller temp. variation due to contactor chattering problem.
What test must you do before powering up a circuit that you have been working on?
How works the AVR in DG Sets Plz explain??????????
In a 3Ph induction motor(old) 6 wires came out from terminal & not mentioned u1,v1,w1,u2,v2 & w2. how can find out the terminals? how can connect to star delta starter??
why the emf of a cell more than the terminal voltage when the cell is delivering current?
how we calculate the dick for a pole?
what happens when we give ac supply to the dc motor?and why?