there is a power transformer 66/11kV in delta-delta
connection has 5 feeder coming out from the secondary side.
One of the feeder in it normally loaded (loaded than other
feeder)and this feeder usually trips with double OCR causing
the bank transformer to trip. Now if the load of this feeder
is put on other transformer then that no problems occurs on
that transformer or the load. However normally all the
test(IR, PI, short ckt, open ckt,grounding test and other )
has been conducted for this but evertything transformer.....
I am not geting what is the actual problem...
Answers were Sorted based on User's Feedback
Answer / parin patel
This thing happened dew to %Z of transformer.lesser the %Z current supplied by transformer will be more.
example:- there are two transformer
transformer 1: 66/11 kv,%Z= 5% ,15 kVA
transformer 2: 66/11 kv,%Z= 7%, 15kVA
If load is constant(same), current supplied by transformer 1 at 11 kv is more than current supplied by transformer 2 at 11 kv.
In your case ,you have to check the value of feeder current when it's supplied by two different transformer.in both case it might be different.
Is This Answer Correct ? | 0 Yes | 0 No |
More data is required for analysis.If the transformers are
of same capacity and relays are identical ,interchange the
relays of transformer banks and watch.
Is This Answer Correct ? | 0 Yes | 0 No |
Hi Friend I am used multimeter to measure the voltage between R Phase(SS1) to R Phase(SS2). In SS1 is connected with UPS loads. But I am getting voltage between these 2 R Phases. Please give some idea friend
What are the various reasons for an inductin motor to get heated?
how do you measure earth leakages in 3phase wires?
What is full form of G.O.D in 11kv distribution?
10 Answers GOD, MSEB, Shyam Indus Power, STL,
how we findout a ignater is faulty or not?
what is saturation kit?which use above 15 kw motors panel side.
What should be the conservator minimum oil level required in 2 mva transformer
What is Servo Ventilated Motor?
difference b/w timer and counter
I have a transformer whose primary operates at 230V, 50Hz for which the secondary voltage will be 12V, 50Hz. What will be the secondary voltage if the primary is fed with 400V, 8KHZ Signal?
Is it possible to run HT motor through LT VFD (LT VFD supply given to Transformer LT side and transformer HT side connected to motor)
what is thermal resistance of PVC Cable.