there is a power transformer 66/11kV in delta-delta
connection has 5 feeder coming out from the secondary side.
One of the feeder in it normally loaded (loaded than other
feeder)and this feeder usually trips with double OCR causing
the bank transformer to trip. Now if the load of this feeder
is put on other transformer then that no problems occurs on
that transformer or the load. However normally all the
test(IR, PI, short ckt, open ckt,grounding test and other )
has been conducted for this but evertything transformer.....
I am not geting what is the actual problem...
Answers were Sorted based on User's Feedback
Answer / parin patel
This thing happened dew to %Z of transformer.lesser the %Z current supplied by transformer will be more.
example:- there are two transformer
transformer 1: 66/11 kv,%Z= 5% ,15 kVA
transformer 2: 66/11 kv,%Z= 7%, 15kVA
If load is constant(same), current supplied by transformer 1 at 11 kv is more than current supplied by transformer 2 at 11 kv.
In your case ,you have to check the value of feeder current when it's supplied by two different transformer.in both case it might be different.
| Is This Answer Correct ? | 0 Yes | 0 No |
More data is required for analysis.If the transformers are
of same capacity and relays are identical ,interchange the
relays of transformer banks and watch.
| Is This Answer Correct ? | 0 Yes | 0 No |
What are the common sources of energy?
how to do CT Burden test
How to select busbar?
how could we know the size of cable by physical view?
0 Answers Havells, United Engineering,
We have 2 no. 4MW DG set. and GEB supply. But, we running, only 1 DG set. when we done APFC/Power factor setting : 0.90, then winding temp. Low. but when setting done : 0.83, then Winding temp. increase. WHY Why ? ? ?, plz give me answer.
1 Ton is equal to how many watts?
Why? We r used 50sq. mm. And above size cable in 3.5 core and below size are used in 4core
plz tel me syllabus and exam date 4 jr executive engg (electrical)
0 Answers AAI Airports Authority Of India,
i need list of swg(standard wire guage) or area of conductor v/s current carrying capacity of conductor copper & alluminium...
what is different between 51N and 51G functions relay?
why we use copper earthing for neutral while for body GI.
1 Answers Chennai Metro Rail Limited CMRL, Valeo Lighting Systems India Private Limited,
why spark is produced in mosquito bat?and what are the ways to reduce it?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)