what is the problem occer in motor
Answers were Sorted based on User's Feedback
Answer / sujit ril
Generally in any motor the following types of problems can
occure in Running condition :
under Voltage ( During motor start ),
over load ( If we couple a pump or compressor over rating
than motor so we put more load on motor during running ),
Some time undercurrent may also.
Rest as Mr. kumar said above winding damage also happen but
it is a physical damage.
All motor those being used in field allways being heated by
some auxilary supply voltage to avoid moisture contamination
on motor winding ( not required during running as being
heated by the main supply voltage ). Otherwise in a long
run the moisture can damage the winding insulation and
winding may be short circuited.
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / g.n.d.kennedy
I think, my friends are correct. However, the following
problems shall be consolidatively considered which would
occur for motors.
1. OVER VOLTAGE
2. OVER LOAD ( that is over curren resulting over heat}
3. disconnect of either one or two phase in case of 3 pahse
motor
4. Phase sequence reversal
5. Over speed
6. Earth fault
Is This Answer Correct ? | 2 Yes | 1 No |
How many different speeds can be obtained in cascade control of two induction motors?
Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient?
What is the importance of earthing?
how can we change the supply voltage?
How to Convert Gen KW to H.T amps ?
What is the effect on Power factor and capacitor when your company load is more than 70 % of welding transformer
In a three-phase full converter, output voltage pulsates at frequency of a. f b. 2f c. 3f d. 6f
Classify drilling machines.
I have 380.KVA Volva Penta DG set. Tell me how to calculate units from KWH reading....
what you mean by current? what you mean by voltage? what is difference between star and delta connection in motor side?
Is it possible to import & export power through the same power transformer? what will be the vector group normally for both different or same?
. Draw the vector diagram and condition for the following: 1) Dyn1 2) Ynd0 3) YnYn0