Our Company's Contract Demand is 110 kVA. We use 12
Capacitors each of 12.5 kVAr Capacity to maintain Power
Factor of 0.99. So, what steps should we take so that our
Contract demand does not exceed 110 kVA?
In order to know how much capacity to use one has to know
what is the now the actual power factor. Let’s say the
actual power factor is 0.8.Then the reactive power is
110*sqrt(1-0.8^2)=66 kVAr.
If the power factor is 0.99 then the reactive power from
the Utility will be 110*sqrt(1-0.99^2)=15.5 kVAr.
You have to compensate the difference 66-15.5=50.5 kVAr so
4*12.5=50 kVAr it is enough.
Is This Answer Correct ? | 7 Yes | 0 No |
what is the acceptable value of TAN DELTA and dissipation factor for 11kV, 1.75HP Motor?.
why open circuit test is conducted on hv side and short circuit test is conducted on lv side of a transformer ?what is the reason for it ?
What is the diff. between single compression and double compression gland
only three phases are coming in step down tranformers.how to get neutral?
What is the alternate solution for testing of polarity by using polarity tester while its milli ammeter does not works?
what will happen if we will not use commutater means if we will give dc to the windings in dc motor
differnce between single acting and double acting solenoid valves
What are the safety equipments you should use while you are in a hvac switch yard
1 Answers GPSC Gujarat Public Service Commission,
We have three 33kv substations. All of them energised by same source.When i am checking the phase sequence between one substation to other substation (like R Phase to R Phase) by multimeter i am getting some voltage.Near to LT panels UPS panels are there. Can u explain whether any possible to happen like that. In Phase SEquencemeter is showing correctly in both substations. How is it happen. Explain me.Explain me communication signal will produce Phase difference on this case.
what is the problem with single phase AC motors and how is it overcome?
i want to ask that as everybody knows that in star connection on star point is called neutral. my question is that why on that poin called neutral. what is the reason behind it. what is the logic behind it. i heared somewhere that on this point all phases current become zero thats why. if this answer is right then prove why on that point is current become zero. if this answer is not right then tell me the right answer. post ur answer here or on my mail address. m.ikram786@yahoo.com m.ikram555@gmail.com. thanks.
For 280kw power. Which cable I can usr