For 300 MW plant what is the distribution voltage
Answers were Sorted based on User's Feedback
Answer / virendra joshi
It depends that receiving station is how far & also how
many feeders are to be taken. if power is 300 MW then HV
transmission is ideal because the conductor size would be
less & hence the cost of transmission is less. if i would
be the designer i use 400 KV 2 nos feeder to receiving
station.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / joel
The distribution voltage is the LV that you will get. Like
for example in a 300MW 138kV/13.8kV substation, 13.8kV line
will go to the building RMU then this will be step down to
380V for distribution by a distribution transformer
installed in the building.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / jagannath swami
Its fully depend upon the switch yard (EB ) how much distance from ur end as per ER 300 MW power gen. upto 220kv S.S. is required . and the distribution is ur hand
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / khader shah
Distribution voltage will be 380 to 460 volts only for a 300
MW plant
| Is This Answer Correct ? | 0 Yes | 1 No |
How shall i design a liquid rotor starter
Iwould like to know barc interview questions
why nearly all voltages are in the multiples of 11?
Please help me regarding my one concern. - During earth pit testing we noticed that the Clean earth pit and dirty earth pit showing continuity (Resistance value - 5ohm) . I want to know that if both earth pit have separate location and there is not internal looping between PIT then why such continuity is showing on it . Because of this issue the field side all earthing point showing short. In PLC panel we are providing two types of earthing cable which is coming from separate earth pit (Clean and Dirty earth pit) because of earth PIT showing short our PLC is not complying spec . please help regarding this issues.
please tell 1 ton equal to how many kilo watt?? in some converter software's that is 3.5 kw. is it right?
we all know voltage is a force(emf), and the force always devides if 2 or more than2 loads are there but why does the voltage remains same is parallel, it must devide na ???
What happens when the field of an alternator connected to infinite bus is suddenly removed?
how many earthing required for ups, what should be the earth voltages
where induction generator is used ?
what is transformer tap change HT side and LT side
HOW CAN YOU CALCULATE PRACTICAL EFFICIENCY OF A ASYNCHRONOUS INDUCTIONMOTOR OF 7.5KW,& MOTOR IS RUNNING WITH AVOLTAGE OF 410 VOLTS,& TAKING CURENT OF 13 AMPS
How can we calculate the transformer rating if the load calculated is 1000KW (11Kv Supply)?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)