For 300 MW plant what is the distribution voltage
Answers were Sorted based on User's Feedback
Answer / virendra joshi
It depends that receiving station is how far & also how
many feeders are to be taken. if power is 300 MW then HV
transmission is ideal because the conductor size would be
less & hence the cost of transmission is less. if i would
be the designer i use 400 KV 2 nos feeder to receiving
station.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / joel
The distribution voltage is the LV that you will get. Like
for example in a 300MW 138kV/13.8kV substation, 13.8kV line
will go to the building RMU then this will be step down to
380V for distribution by a distribution transformer
installed in the building.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / jagannath swami
Its fully depend upon the switch yard (EB ) how much distance from ur end as per ER 300 MW power gen. upto 220kv S.S. is required . and the distribution is ur hand
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / khader shah
Distribution voltage will be 380 to 460 volts only for a 300
MW plant
Is This Answer Correct ? | 0 Yes | 1 No |
Why different types of connection in transformers are used? (star/star,star/delta,delta/star,delta/delta)Why we are only taking in consideration of star/delta type transformers? if only star/delta is good in practice where doses other type of transformers are used? Note: i want to know place of using different types of transformers other than Star/delta type with brief description.
Uses of induction motor
what is a lightning arrester???
what is the role of energy meter in distribution system ?
what is the difference between inverter and ups & what is the earth resistance for ups , if its high why so
how can we minimize the off load losses of a distribution transformer which is required to be energized 24x7 ?? capacity of the T/F is 1250 KVA and off load losses are around 2.0 KW.. can we use capacitor bank at the secondary of such a T/F to overcome off load losses? please elaborate briefly...thanks
what is the step by step formula for calculating bus bar phase and neutral size of a panel board.suppose the incomer of panel board is 100A..???step by step answer please
what is meant by ceiling voltage, ceiling current?? pl reply asap
dear friends plz send link about reluctance & universal motor .thank u
what is the procedure to carry out BDV test of a transformer ?
1,Building containing 25 flats how much Amp 3 pole MCCB are required? 2, For the safey of each flat how many Amp RCCB can install -loaded with A/C
what is KA rating and how can we choose switchgears on applications