Difference between DOL starter & star Delta Starter? And
where the Dol starter used upto how much HP and whereas
Star Delta vice versa?
Answers were Sorted based on User's Feedback
Answer / tamil arasu
DOL STARTER STARTING CURRENT IS HIGH.DOL HAVE IN STARTING
TIME MORE THEN 3 TIMES OF NOMINAL CURRENT.BUT S/D STARTER
STARTING CURRENT IS LOW.DOL STARTER NEED 1 CONTACTOR AND
1OLR, S/D NEED 3CONTACTORS,TIMER AND 1OLR FOR FULLY
AUTOMATIC.SEMI S/D NOT NEED FOR TIMER.
UPTO 5 H.P DOL STARTER USED.AND MORE THEN 5H.P USED S/D
STARTER.BUT DOL STARTER ALSO USED FOR ABOVE 15 H.P
ACCORDING TO THE LOAD.INCASE OF WE USING 10H.P MOTOR FOR
WATER PUMP WE HAVE SELECTING DOL AND WE USING FOR SAME H.P
MOTOR FOR MILL WE SELECTING STAR/DELTA.
Is This Answer Correct ? | 24 Yes | 1 No |
Answer / govindaraj
upto 5 hp dol starter is used.
upto 25 hp star delta starter is used
Is This Answer Correct ? | 16 Yes | 11 No |
Answer / guest
On DOl Starter it needs one Magnetic Contractor and in Star
Delta Starter it needs three magnetic Contractor
Is This Answer Correct ? | 11 Yes | 8 No |
please tell me how a surge protector work on a DC 48Volt.? please describe briefly.
what is LOS(line of sight)?
How to know the following data of synchronous generator 1. D-Axis Unsaturated Reactance 2. D-Axis Unsaturated Transient Reactance 3. D-Axis Unsaturated Sub - Transient Reactance
Myself completed B.Tech ECE in private university but i am working as an testing and commissioning engineer in electrical field whether i am eligibility to apply electrical licence.
What is the difference between Droop vs Isoch Control?
can i use the six sigma method which is used in management area, in state estimation of power systems?
What are Line losses and how can be it minimized/controlled.?
I have two AC generators, the first rated 2680KVA for 380V/4345A/pf:0.7 and the second rated 3461KVA for 5500V/363A/pf:0.8. I want to parallel the two generator to a bus. The second generator passes through a transformer to down the voltage to 380V and a part of its power goes to another bus so that it's only a part of the total power of the second generator taht goes to the considered bus. I have two Basler DECS100 AVR regulator. How can I make the synchronization ? What others equipments must have ?
what will be happened when a single phase motor is supplied by the dc supply
WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL
how is the incoming cable size calculated for a given current rating of a panel??
What kind of preventive maintenance are there for AC generator?