how we can select MCB ratings according to Voltages, Curves.
Answer Posted / balakrishnan
1.We can select the MCB's acoording to Voltage is simple,if
we want 230V,select single pole MCb's else want 415V select
3 pole MCB's.
2.We can select the MCB's according to to Curves is also
simple,there are several types of curvature available..
there are,
B type: react quickly overload i.e 3-4.5 times of full load
current
Type C: react more slowly,these are recommended for
inductive with high inrush currents like fluorescent lamp.5-
10 times of Ifl
Type D: 10-20times of Ifl,recommended for very high inrush
current.
Type K: 8-12 times of full load I,recommended for cable
protection to be provided which include
motors,capacitors,and transformers
Type S: 13-17 times of Ifl,recommended for protection of
control Transformer,
Type Z:
Is This Answer Correct ? | 31 Yes | 2 No |
Post New Answer View All Answers
what is the path of thunderlightening? once both a buffalo and a person were standing 5m apart but lightening hit and killed buffalo not person?
why we use the 100% and 95% stator earth fault protection for the synchronus generator ?
how to measure dc earth leakage current?
What is the difference between shortcircuit current, rated current of cable & MCB with example? What will be the size of cable required for 5.5 KW motor (Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.
what are the applications of transistors with low dc gain, high dc gain and medium dc gain( beta)?
How much earthing frequency is capable?
sir i am apearing for nic exam.i dont know exam pattern.can you please send me some model papers
We have Diesel generator of 200KW. fuel consumption is always same,even connected light load or full load. Is it right?
Why Ac Systems Are Preferred Over Dc Systems?
Differentiate between magnetic field and magnetic flux?
What are the different circuits in thermal power plant?
1 hp is equal to how much watt?
which type of effect of turbine and generator reverse power protection ?
how much excitation voltage required to generate 1mw power?
what is motor capacity of 80TR chiller? and also say what is the formula related temperature, motor capacity, TR?