What is difference between miniture circuit breaker and
module case circuit breaker up to 63Amp.
Answers were Sorted based on User's Feedback
MCB can be used for only over current triping.
MCCB can be used for over current and earth fault(in built)
triping.
| Is This Answer Correct ? | 14 Yes | 4 No |
Answer / petrit hajrizi
Can we use MCCB to protect the cable for termal and short
cicuit.
| Is This Answer Correct ? | 5 Yes | 1 No |
MCB- is genarally used for lighting, it is fixed Rating
like: 2A, 6A, 10A,16A,20A,32A,63A. it will trip at any time
current carrying more then its rating.BUT MCCB- is genaraaly
using for Power sources, it is working range of current.
like: 4 -6A, 6-10A, 10-16A. it will use for Varies settings
have to set.
| Is This Answer Correct ? | 5 Yes | 2 No |
And also difference in short circuit current carrying
capacity.MCB having max up to 25kA. MCCB having up to 50KA.
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / pgr ram
MCbs can withstand fault current upto 9KA. whereas MCCBs
can withstand high fault current upto 100ka. Hence MCCBs
are recommended to install at high current distribution
systems. Whereas MCBS are used for feeder distribution.
MCCB cost very high when compared to MCB
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / abracadabra
the difference between mcb and mccb is the difference of
adjusting tripping characteristics. this adjustment is
possible in mccb. the higher current making and breaking
capacity is one of the difference but the main reason is
the tripping char adjustment.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / timbadiya dixit
MCB is use only for over Load protection and MCCB is use to
over load and under load protection And MCCB is one types
of circuit Brecker.
| Is This Answer Correct ? | 3 Yes | 7 No |
what is meant by IGBT how they differ from tyristor ?
what are the main parts of DG? explian thier functions?
8 Answers Apollo Power, Tata DoCoMo, Tyco, Vizag Steel,
What are ampers.30kw motor.440volts.
Explain why machinery used on a.c supply is usually rated in KVA instead of KW?
why one side of tubelight glows after switch off ?
why wave traps are placed only at y and r phase?
What it is the diff btw Package & PEC AC's????
why we can use 1 to 5V dc
What is q factor?
why are distributed windings generally used in alternators?
6 MVA transformer secondary is rated for 725V at no load. The incommer ACB is rated at 690 V, 3200 Amp. Would there be any effect on performance of ACB due to lower voltage rating?
WHAT SHOULD BE THE BEST CURRENT RATINGS (PRIMARY / SECONDARY)FOR A CT INSTALLED AT THE INCOMING 11KV PANE? WILL IT BE CALCULATED ON THE BASES OF MAXIMUM DEMANT VALUE OR ON SUM OF ALL TRANSFORMER'S KVA? NOMALLY MAX DEMAND REPRESENT THE MAXIMUM OPERATING LOAD OF THE PLANT AND TOTAL KVA OF (SAY 5 NUMBERS TRANSFORMERS) REPRESENT THE CONNECTED LOAD. WHICH i.e. MAX DEMAND KVA OR CONNECTED KVA ARE BETTER TO USE FOR CT CURRENT CALCULATION? PLEASE ANSWER.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)