why do we prefer a 3-phase delta connected load rather than
star connected?
Answers were Sorted based on User's Feedback
In star speed of motor is very low with low amp.
and in delta motor running with its normal rated speed with
rated amp.
So generally for motor starting purpose star used and
afterthat its change over to delta
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / nithi
for a same power rating the current in delta connected load
is 1.732 times lesser than the star connected load (heat
loss is less) &also if one phase get opened the other two
phases will serve the load i.e.good stability.but in safety
point of view, star connected load is better than delta
load.because earthing can be done without the help of
earthing transformer.
| Is This Answer Correct ? | 3 Yes | 1 No |
Dear Subhash
Yes speed of motor will remain same in star and delta both
| Is This Answer Correct ? | 0 Yes | 2 No |
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
Earth Resistivity
when we r using 3.5 cable for a bldg. and put laod on each phase using the neutral and neutral is the return paht for the phase so the current of the neutral must be Ir+Ib+iY (return).But the size of the netural is .5 as comper to the phase.
capacitor is load free component but why ampare meter shows current when capacitor bank breaker close?
Explain Need of a starter in a dc motor.? Also explain any two starting and speed control method of dc motor?
what is ht breaker
Can you used moeller lzm1 mccb in a dc system with 125vdc and 20ka short circuit current , beside is it have 24 or 48 volt shunt ? Beside how long current can through from An MCB shunt contacts? (like Z7-AS 24 V)?
Whar is the KvA rating of 33Kv substation & actual kv rating of power generaating station.
I have 1 KW, 3ph. 440v, 50 hz, cos(phi) .75, efficiency 75%(star delta connection)Motor. How to calculate line current & Phase current (1) Star connection (2) delta Connection
WHAT IS THE DIFFERANCE BETWEEN IP54 AND IP55
What are protection of power transformer?
Show formula which gives full load current 4.8 amps of a 3 HP motor and 27 amps of a 20 HP motor having 3 phase 460 volts, 0.8 Pf.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)