Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


can we done C.T.sc at output?
if yes y,if no y?

Answers were Sorted based on User's Feedback



can we done C.T.sc at output? if yes y,if no y?..

Answer / satyabrata

i agree with manmohan's answar.but another reason is if ct secondary will open ckt then the ct core will saturated causing heavy iron loss & will induce high voltage in secondary.which will cause a shock on operating personel.

Is This Answer Correct ?    7 Yes 1 No

can we done C.T.sc at output? if yes y,if no y?..

Answer / manmohan

Unless a burden (i.e. meters, relays, etc.) is connected to
the CT, current transformers should always be shorted
across the secondary terminals. The reason is very high
voltages will be induced at the terminals. CT Secondary has
high resistance so it can be short circuited.

Is This Answer Correct ?    5 Yes 0 No

can we done C.T.sc at output? if yes y,if no y?..

Answer / raju4472

yes, i agree both the answers and if CT is saturated after
high voltage on secondary, then there will be short circuit.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Why cannot we insulate HT over head cable to avoid ionization of air around the HT Cable?..By this we can minimise corona loss also..

1 Answers  


How much ampere can withstand for 2sq mm c able?

2 Answers  


In Power Line Communication (PLC) the wave trap is used to block communication signals from entering neighboring lines. My question is this: Why do they allow for different filtering arrangements on these wave traps? Isn't it always going to be a low pass filter since we want the power frequency to go through, and the comm signal blocked?

0 Answers  


Energy metering: On the property I am renting, the supply voltage is 2 x 110 volts. These 2 x phases enter a energy meter which then exit the meter to over head lines to my house. Question 1. The meter is single phase 240 volts but is being used as 2 x phase(2 x 110volt), is this acceptable? if not, please give me the reasons. The meter details are as follows: 60Hz 15amp Imax 100 amp Kd 3,6 Wh/R 1 fase 3 hilos Model FX 231. I think it was manufactured in Brasil From this meter, the cables run along over head aluminum conductors,I estimate the cross sectional area to be 25mm diameter, but the neutral is only about 10mm square diameter, which cover a distance of 170 meters and then terminate with an underground cable of 65 meter length, total length = 235 meters. There must be a huge voltage drop over this length. This line is protected with 2 x 200 amp aluminum fuses after the meter, there is no main switch in the distribution board. These 2 phases connect directly onto 2 busbars. Surely the neutral should be the same size as the conductors if not more? Question2. What are your thoughts about this installation, should there be better protection, is the neutral too small? During the night, the lights dim then brighten all the time, this cannot be good for my electrical appliances. In my home, I only have a small electric geyser and fridge, my stove works off gas. But when i use other appliances like the washing machine or microwave oven, the light dim. The internal wiring of this house is done with solid hard drawn copper wires and of course, they have to be under rated. I am a retired electrician by trade, but not on the metering and over head mains side, my experience is on the factory maintenance side of things. Your expertise on these matters will be greatly appreciated. Please inform me how to rectify or make any improvements Kind regards, my power bill is very expensive, so I need to know how to bring it lower. Kind regards, Brian

1 Answers  


What is the difference b/w earthing & grounding?

6 Answers  


i completed my DEEE. and i want to electrical c license. how to get it..?

0 Answers  


What is the effect of impedance on the heat losses in case of AC system??? Does heat losses really depends on the impedance or depends only on resistive component only..??

4 Answers  


why white color LED light is not possible?

1 Answers  


How much KVAr bank reqired for 630 KVA transformer on full load for maintain power factor upto.99

4 Answers   Dhanalakshmi Industries, DLF,


how can testing using megger?

1 Answers  


what is the differnce between ac and dc?

5 Answers  


wich type of cable is selected for wiring of 20hp motor?

5 Answers   Alchemist,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)