Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calculate the electrical load for a standard telecom
BTS shelter and capacity of DG set required to cater to
this load?

Answers were Sorted based on User's Feedback



How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set req..

Answer / gkg

For Active load,voltage will be 48vdc or 24vdc,
so total active load=48v x 28A =1344w =1.34kw

passive load calc ok.

Is This Answer Correct ?    51 Yes 10 No

How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set req..

Answer / chandrashekar

Generally in telecom shelter only Passive and Activie load
will be available.
Passive loads are battery bank, PIU and Power plant. and In
active loads Concern BTS and Transmission load.

Thumb rule to calculate DG rating is KW=KVA*PF(0.8) or
Efficiency

i.e KVA=KW/PF


Example to calculate the rating of DG.

If total Load is available 15Kw both active and Passive
then

we should apply above formula KW=KVA*0.8

15=KVA*0.8 KVA = 15/0.8=18.75KVA
we can consider nearest rating of DG i.e=20KVA








Active Load Calculation:

Say a shelter is having only 1nos of BTS,Each BTS will
consume 20A to 30A load current depends up on type and make
of the BTS. average if we take 25A.
Transmission load for each BTS is about 3A total
transmission load current is 3A.
Now the Total Active Load current is =25+3=28A

Total Active load is P=VI P=230*28=6.4KW

Passive Load Calculation
1) AC Unit 2tr 1No the load is =7KW
2) All Internal Lighting and other =1KW
total passive load is 8KW now the toatl active and passive
load is =6.4+7+1= 14.4 KW round off 15KW.
for 15KW load 20KVA Dg set is sufficient

NOTE: always we should consider 1.5% extra rating because
starting current will always 1.5 % higher than load current.

Is This Answer Correct ?    56 Yes 25 No

How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set req..

Answer / dhananjay vats

VXI(BTS LOAD)=W/1000=KW.....A
8% LOAD LOSSES IN KW.........B
10% B.B CHARGING LOAD (EX-600AH, 60AX54V/1000)....C
INCOMING LOAD IN KW....C
AC IN KW (EX-1TR, 1TR-1350W, 1.3KW)......D
TOTAL ADD IN KW=A+B+C+D.....CONNECTION EB IN KW
KW=KVA/P.F

Is This Answer Correct ?    4 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

how to find number of run for transformer & alternator secondary side? give the example.

2 Answers   Powergear, Regen Powertech,


why we dont store the ac power in battery?

1 Answers   TCS,


what are the dimensions for 200 kva transformer plinth (plateform),in which pcc m20 is used..

1 Answers   UPPCL,


why make protection 85% of winding?

1 Answers  


what is difference between fuse and breaker?

6 Answers   ABB,


what is cut out fuse?

1 Answers  


As a good company employee, can you report your supervisor to the company management if he or she is going against the company interest in his or her actions?

1 Answers   MAHINDRA,


If one ct is reversely connected in Y system what will effect in kwh and kvarh meter?

1 Answers  


Earth Resistivity

2 Answers  


The transmission does not have options: a)Partition noise b) Flicker noise c) resistance d) Short noise and reason

0 Answers  


In the diesel generator if there is an AVR (auto voltage regulator) gone faulty, in this condition is there any way to generate the voltage from the alternator? I need a brief explanation can you please help somebody

1 Answers   Vodafone,


Is it possible that Generator trip but Turbine not trip.Give explanation.

1 Answers   Essar,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)