How to calculate the electrical load for a standard telecom
BTS shelter and capacity of DG set required to cater to
this load?
Answers were Sorted based on User's Feedback
Answer / gkg
For Active load,voltage will be 48vdc or 24vdc,
so total active load=48v x 28A =1344w =1.34kw
passive load calc ok.
Is This Answer Correct ? | 51 Yes | 10 No |
Answer / chandrashekar
Generally in telecom shelter only Passive and Activie load
will be available.
Passive loads are battery bank, PIU and Power plant. and In
active loads Concern BTS and Transmission load.
Thumb rule to calculate DG rating is KW=KVA*PF(0.8) or
Efficiency
i.e KVA=KW/PF
Example to calculate the rating of DG.
If total Load is available 15Kw both active and Passive
then
we should apply above formula KW=KVA*0.8
15=KVA*0.8 KVA = 15/0.8=18.75KVA
we can consider nearest rating of DG i.e=20KVA
Active Load Calculation:
Say a shelter is having only 1nos of BTS,Each BTS will
consume 20A to 30A load current depends up on type and make
of the BTS. average if we take 25A.
Transmission load for each BTS is about 3A total
transmission load current is 3A.
Now the Total Active Load current is =25+3=28A
Total Active load is P=VI P=230*28=6.4KW
Passive Load Calculation
1) AC Unit 2tr 1No the load is =7KW
2) All Internal Lighting and other =1KW
total passive load is 8KW now the toatl active and passive
load is =6.4+7+1= 14.4 KW round off 15KW.
for 15KW load 20KVA Dg set is sufficient
NOTE: always we should consider 1.5% extra rating because
starting current will always 1.5 % higher than load current.
Is This Answer Correct ? | 56 Yes | 25 No |
Answer / dhananjay vats
VXI(BTS LOAD)=W/1000=KW.....A
8% LOAD LOSSES IN KW.........B
10% B.B CHARGING LOAD (EX-600AH, 60AX54V/1000)....C
INCOMING LOAD IN KW....C
AC IN KW (EX-1TR, 1TR-1350W, 1.3KW)......D
TOTAL ADD IN KW=A+B+C+D.....CONNECTION EB IN KW
KW=KVA/P.F
Is This Answer Correct ? | 4 Yes | 1 No |
for measuring current and etc.,why we use value of 1.732 in three phase calculation. not in single phase.why
Working of furnace in detail...?
how can we make cable shedule for controll wiring ? which details must be required for it.?
why in transformer there is not rotating fiddl/ magnetic field like motor
1. Why a DC motor starter is called 3 point starter
21 Answers ABB, CG, College School Exams Tests, Crompton Greaves, Infosys, Siva,
The transformer which is smallest in size is and how to calculate that? The options are 100 KVA, 50 Hz 100 KVa, 100 Hz 100 KVA, 25 Hz 50KVA, 25 HZ
4 Answers Ranbaxy, Zee Laboratories,
Why Ac Systems Are Preferred Over Dc Systems?
if the HR asked to me., you have got 92% in higher secondary but got only 72% in engg whats the reason??what should i have to say ..please help me..
The principle of switching circuits for different types of batteries in application of storage systems
Pls explan the OLR setting in VCB at HT yard
short circuit test of transformer gives what?
What is power transformer?