How to calculate the electrical load for a standard telecom
BTS shelter and capacity of DG set required to cater to
this load?
Answers were Sorted based on User's Feedback
Answer / gkg
For Active load,voltage will be 48vdc or 24vdc,
so total active load=48v x 28A =1344w =1.34kw
passive load calc ok.
Is This Answer Correct ? | 51 Yes | 10 No |
Answer / chandrashekar
Generally in telecom shelter only Passive and Activie load
will be available.
Passive loads are battery bank, PIU and Power plant. and In
active loads Concern BTS and Transmission load.
Thumb rule to calculate DG rating is KW=KVA*PF(0.8) or
Efficiency
i.e KVA=KW/PF
Example to calculate the rating of DG.
If total Load is available 15Kw both active and Passive
then
we should apply above formula KW=KVA*0.8
15=KVA*0.8 KVA = 15/0.8=18.75KVA
we can consider nearest rating of DG i.e=20KVA
Active Load Calculation:
Say a shelter is having only 1nos of BTS,Each BTS will
consume 20A to 30A load current depends up on type and make
of the BTS. average if we take 25A.
Transmission load for each BTS is about 3A total
transmission load current is 3A.
Now the Total Active Load current is =25+3=28A
Total Active load is P=VI P=230*28=6.4KW
Passive Load Calculation
1) AC Unit 2tr 1No the load is =7KW
2) All Internal Lighting and other =1KW
total passive load is 8KW now the toatl active and passive
load is =6.4+7+1= 14.4 KW round off 15KW.
for 15KW load 20KVA Dg set is sufficient
NOTE: always we should consider 1.5% extra rating because
starting current will always 1.5 % higher than load current.
Is This Answer Correct ? | 56 Yes | 25 No |
Answer / dhananjay vats
VXI(BTS LOAD)=W/1000=KW.....A
8% LOAD LOSSES IN KW.........B
10% B.B CHARGING LOAD (EX-600AH, 60AX54V/1000)....C
INCOMING LOAD IN KW....C
AC IN KW (EX-1TR, 1TR-1350W, 1.3KW)......D
TOTAL ADD IN KW=A+B+C+D.....CONNECTION EB IN KW
KW=KVA/P.F
Is This Answer Correct ? | 4 Yes | 1 No |
What is function of inverter? and who it's operate & what are controlling devices are used?
Why resistance is not measure in running conditions of motor
Wat is the best to use in a generator a 6.5kva or a 7 kw
what is the difference between Earth and neutral? and what is the difference between ground earthing and neutral earthing?
what is meant by Back emf ?where its occur ?
How to calculate earth fault current for 6.6 KV , 50 HZ , 756 Amps , 3000 RPM , 0.8 PF generator
which generator is called as brushless excitation generator and why??
why mosquito bat makes noise when it hits with a insect?
Sir, I m 3rd year student 4m DCE and want to do internship in siemens or l&t or any other mnc related to electrical engineering. please tell me the procedure 4 same and oblige me
I want to do a mini project. Now I'm studying in 6th semis tor EEE Engineering.
wt wil happen if a 120kv line is grounded
What are the factors considered for the selection of cable?