How to calculate the electrical load for a standard telecom
BTS shelter and capacity of DG set required to cater to
this load?
Answers were Sorted based on User's Feedback
Answer / gkg
For Active load,voltage will be 48vdc or 24vdc,
so total active load=48v x 28A =1344w =1.34kw
passive load calc ok.
| Is This Answer Correct ? | 51 Yes | 10 No |
Answer / chandrashekar
Generally in telecom shelter only Passive and Activie load
will be available.
Passive loads are battery bank, PIU and Power plant. and In
active loads Concern BTS and Transmission load.
Thumb rule to calculate DG rating is KW=KVA*PF(0.8) or
Efficiency
i.e KVA=KW/PF
Example to calculate the rating of DG.
If total Load is available 15Kw both active and Passive
then
we should apply above formula KW=KVA*0.8
15=KVA*0.8 KVA = 15/0.8=18.75KVA
we can consider nearest rating of DG i.e=20KVA
Active Load Calculation:
Say a shelter is having only 1nos of BTS,Each BTS will
consume 20A to 30A load current depends up on type and make
of the BTS. average if we take 25A.
Transmission load for each BTS is about 3A total
transmission load current is 3A.
Now the Total Active Load current is =25+3=28A
Total Active load is P=VI P=230*28=6.4KW
Passive Load Calculation
1) AC Unit 2tr 1No the load is =7KW
2) All Internal Lighting and other =1KW
total passive load is 8KW now the toatl active and passive
load is =6.4+7+1= 14.4 KW round off 15KW.
for 15KW load 20KVA Dg set is sufficient
NOTE: always we should consider 1.5% extra rating because
starting current will always 1.5 % higher than load current.
| Is This Answer Correct ? | 56 Yes | 25 No |
Answer / dhananjay vats
VXI(BTS LOAD)=W/1000=KW.....A
8% LOAD LOSSES IN KW.........B
10% B.B CHARGING LOAD (EX-600AH, 60AX54V/1000)....C
INCOMING LOAD IN KW....C
AC IN KW (EX-1TR, 1TR-1350W, 1.3KW)......D
TOTAL ADD IN KW=A+B+C+D.....CONNECTION EB IN KW
KW=KVA/P.F
| Is This Answer Correct ? | 4 Yes | 1 No |
Please sent me some previous year question papers of BSNL-JTO telecom and RRB in ELectrical Engineering to varshashahi@yahoo.com
Classify milling machines.
we often use the word HT (high tension) line.or we say HT switch gear, whats does HT basically mean. is it different from high voltage.
what is cogging in motors?
What can make the the overloads operate when a star delta three phase motor starts?
How can you test the vector group of power transformers?
In a 11Kv/433Volt Delt-star step down transformer one one line(Line-B) of HT site is open & earthed on DP structur. What will be the voltage on LT side R-Y, Y-B,B-R and R-N, Y- N & B-N?. Please help to understand the problem with examples. Arvind , Jaipur.
What is the armature mmf in a D.C machine?
What type of pipe material G.I or M.S is used for sprinkler system?
how to measure genset CT coil range?
importance of air gap in transformer
Difference between divercity and power factor
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)