Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calculate the electrical load for a standard telecom
BTS shelter and capacity of DG set required to cater to
this load?

Answers were Sorted based on User's Feedback



How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set req..

Answer / gkg

For Active load,voltage will be 48vdc or 24vdc,
so total active load=48v x 28A =1344w =1.34kw

passive load calc ok.

Is This Answer Correct ?    51 Yes 10 No

How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set req..

Answer / chandrashekar

Generally in telecom shelter only Passive and Activie load
will be available.
Passive loads are battery bank, PIU and Power plant. and In
active loads Concern BTS and Transmission load.

Thumb rule to calculate DG rating is KW=KVA*PF(0.8) or
Efficiency

i.e KVA=KW/PF


Example to calculate the rating of DG.

If total Load is available 15Kw both active and Passive
then

we should apply above formula KW=KVA*0.8

15=KVA*0.8 KVA = 15/0.8=18.75KVA
we can consider nearest rating of DG i.e=20KVA








Active Load Calculation:

Say a shelter is having only 1nos of BTS,Each BTS will
consume 20A to 30A load current depends up on type and make
of the BTS. average if we take 25A.
Transmission load for each BTS is about 3A total
transmission load current is 3A.
Now the Total Active Load current is =25+3=28A

Total Active load is P=VI P=230*28=6.4KW

Passive Load Calculation
1) AC Unit 2tr 1No the load is =7KW
2) All Internal Lighting and other =1KW
total passive load is 8KW now the toatl active and passive
load is =6.4+7+1= 14.4 KW round off 15KW.
for 15KW load 20KVA Dg set is sufficient

NOTE: always we should consider 1.5% extra rating because
starting current will always 1.5 % higher than load current.

Is This Answer Correct ?    56 Yes 25 No

How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set req..

Answer / dhananjay vats

VXI(BTS LOAD)=W/1000=KW.....A
8% LOAD LOSSES IN KW.........B
10% B.B CHARGING LOAD (EX-600AH, 60AX54V/1000)....C
INCOMING LOAD IN KW....C
AC IN KW (EX-1TR, 1TR-1350W, 1.3KW)......D
TOTAL ADD IN KW=A+B+C+D.....CONNECTION EB IN KW
KW=KVA/P.F

Is This Answer Correct ?    4 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage from 33kv to 415v directly using single transformer.

12 Answers   ABB, Adani, Central Electricals, Electrical, HCL,


What will be the current rating of Main switch for 80 kVAR panel

1 Answers  


what is the difference b/w neutral and ground?

4 Answers  


How to calculate cable size for a particular load? i have 12 MW,11KV Motor 3 Phase, what should be cablesize? What are the points to remember for cable sizing calculations?

2 Answers  


What Is the Difference Between Lightening Spike and Lightening Arrester?

1 Answers  


how we select ac fuse rating of an power inverter???

0 Answers   Simco,


sugest any typical project ?

0 Answers  


why we multiply 11 in High Electric supply?(eg.11KV, 33Kv, 330Kv etc.)

3 Answers  


What is Cement

11 Answers   ACC, L&T, Reliance Cement,


Which type of alternator used in power station?

2 Answers  


Is there any difference in AC current/ DC current carrying capacity of a conductor .What can be maximum current handling capacity of a 2.5mm stranded cu cable when connected to AC and DC supply.

1 Answers  


what kvrah y we need to take the readind of that

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)