How to calculate the electrical load for a standard telecom
BTS shelter and capacity of DG set required to cater to
this load?
Answers were Sorted based on User's Feedback
Answer / gkg
For Active load,voltage will be 48vdc or 24vdc,
so total active load=48v x 28A =1344w =1.34kw
passive load calc ok.
| Is This Answer Correct ? | 51 Yes | 10 No |
Answer / chandrashekar
Generally in telecom shelter only Passive and Activie load
will be available.
Passive loads are battery bank, PIU and Power plant. and In
active loads Concern BTS and Transmission load.
Thumb rule to calculate DG rating is KW=KVA*PF(0.8) or
Efficiency
i.e KVA=KW/PF
Example to calculate the rating of DG.
If total Load is available 15Kw both active and Passive
then
we should apply above formula KW=KVA*0.8
15=KVA*0.8 KVA = 15/0.8=18.75KVA
we can consider nearest rating of DG i.e=20KVA
Active Load Calculation:
Say a shelter is having only 1nos of BTS,Each BTS will
consume 20A to 30A load current depends up on type and make
of the BTS. average if we take 25A.
Transmission load for each BTS is about 3A total
transmission load current is 3A.
Now the Total Active Load current is =25+3=28A
Total Active load is P=VI P=230*28=6.4KW
Passive Load Calculation
1) AC Unit 2tr 1No the load is =7KW
2) All Internal Lighting and other =1KW
total passive load is 8KW now the toatl active and passive
load is =6.4+7+1= 14.4 KW round off 15KW.
for 15KW load 20KVA Dg set is sufficient
NOTE: always we should consider 1.5% extra rating because
starting current will always 1.5 % higher than load current.
| Is This Answer Correct ? | 56 Yes | 25 No |
Answer / dhananjay vats
VXI(BTS LOAD)=W/1000=KW.....A
8% LOAD LOSSES IN KW.........B
10% B.B CHARGING LOAD (EX-600AH, 60AX54V/1000)....C
INCOMING LOAD IN KW....C
AC IN KW (EX-1TR, 1TR-1350W, 1.3KW)......D
TOTAL ADD IN KW=A+B+C+D.....CONNECTION EB IN KW
KW=KVA/P.F
| Is This Answer Correct ? | 4 Yes | 1 No |
why we step down voltage level from 33kv to 11kv and 11kv to 415v.Instead we can step down voltage from 33kv to 415v directly using single transformer.
12 Answers ABB, Adani, Central Electricals, Electrical, HCL,
What will be the current rating of Main switch for 80 kVAR panel
what is the difference b/w neutral and ground?
How to calculate cable size for a particular load? i have 12 MW,11KV Motor 3 Phase, what should be cablesize? What are the points to remember for cable sizing calculations?
What Is the Difference Between Lightening Spike and Lightening Arrester?
how we select ac fuse rating of an power inverter???
sugest any typical project ?
why we multiply 11 in High Electric supply?(eg.11KV, 33Kv, 330Kv etc.)
What is Cement
11 Answers ACC, L&T, Reliance Cement,
Which type of alternator used in power station?
Is there any difference in AC current/ DC current carrying capacity of a conductor .What can be maximum current handling capacity of a 2.5mm stranded cu cable when connected to AC and DC supply.
what kvrah y we need to take the readind of that
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)