Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


1.In two wattmeter method if one wattmeter shows Negative
reading then wat is reason?
2.Wat is the reason for low voltage in houses?
3.Wat is meant by current and voltage? wat is difference
between the two?

Answers were Sorted based on User's Feedback



1.In two wattmeter method if one wattmeter shows Negative reading then wat is reason? 2.Wat is t..

Answer / dileep

two watt meter method is used in measurement of power under un balanced condition.there are two reasons for - ve value
1). if load consist of more inductivd or capacive load with negligible resistive then it will show _ve value .pf angle is more than 65 deg
. in case of induction motor no load test one of the watt meter will indicate _ve because no load pf is 0.2 lag pf angle is nearer to 75 deg
2).reverse. connections of current coil

Is This Answer Correct ?    98 Yes 6 No

1.In two wattmeter method if one wattmeter shows Negative reading then wat is reason? 2.Wat is t..

Answer / max

1)hmm exacly opp
that means pf of load is less than 0.5 but greater than 0
2)load unbalance inductive load(?)
3)voltage -cause n current -effect

Is This Answer Correct ?    49 Yes 20 No

1.In two wattmeter method if one wattmeter shows Negative reading then wat is reason? 2.Wat is t..

Answer / sanjoy

5.Yes. It’s possible one wattmeter may indicate a negative value. One Wattmeter will read negative watts if the power factor goes below 0.5 .

Is This Answer Correct ?    24 Yes 4 No

1.In two wattmeter method if one wattmeter shows Negative reading then wat is reason? 2.Wat is t..

Answer / nitin banegaon

its sooo simlpe. when induction motor is on load then the no load current will have two components one is active/load component and other magnetizing component. Magnetizing component is for creating magnetic field to spin the motor which is independent of load current and it lags behind the voltage by 90. Initially on load, current is so small which is normally is in phase with applied voltage. So on no load circuit is inductive. So power factor is small nearly 0.2 to 0.4.

Is This Answer Correct ?    8 Yes 1 No

1.In two wattmeter method if one wattmeter shows Negative reading then wat is reason? 2.Wat is t..

Answer / syam kumar

2.reasion due to low voltage in houses is, in our street
poles we have generally 3 phase wires and 1 neutral
wire.every house connected to 1 phase and neutral wire.if
more number of houses connected by same phase then those
are effected from this low voltage problem.so some houses
will have power and some houses effected from this low
voltage. so if we connect equal distribution to all phases
this effect is reduced. this connection will given by our
linemen.
3.flow of charge is current
and potential difference between any two points in a
conductor is called voltage.
voltage and current are combinational.

Is This Answer Correct ?    6 Yes 4 No

1.In two wattmeter method if one wattmeter shows Negative reading then wat is reason? 2.Wat is t..

Answer / kd

1.power flow is in the reverse direction
2. Power factor is less than 0.5

Thanks !

Is This Answer Correct ?    2 Yes 0 No

1.In two wattmeter method if one wattmeter shows Negative reading then wat is reason? 2.Wat is t..

Answer / james nyoro

1;phase angle is greater than 90 degrees cos 90=0 cos-in
=math error
2;reverse connection of current coil

Is This Answer Correct ?    2 Yes 7 No

1.In two wattmeter method if one wattmeter shows Negative reading then wat is reason? 2.Wat is t..

Answer / kaushik patel

But how measure it negative value. That is below in 0. And the pointer go to below zero and below zero not mention calibration then how measure it?

Is This Answer Correct ?    0 Yes 5 No

1.In two wattmeter method if one wattmeter shows Negative reading then wat is reason? 2.Wat is t..

Answer / guest

pf of the load is greater than 0.5..

Is This Answer Correct ?    44 Yes 54 No

1.In two wattmeter method if one wattmeter shows Negative reading then wat is reason? 2.Wat is t..

Answer / vikas

because in wattmeter there r two internal winding i.e., m
and c which need to be short . if ther are not short then
one wattmeter shows negative value.

Is This Answer Correct ?    5 Yes 44 No

Post New Answer

More Electrical Engineering Interview Questions

why the indian frequency is 50 hz & U.S.Frequency of 60 hz

3 Answers  


synchronous motor of 13.5MW having which type protection? and how to set relay?give me relay setting calculation for different protection for this motor assume efficiency,power factor and other term if neccecery

1 Answers  


what is the generator rating for 40 amp load of 3phase motor.?? 400v voltage of generator... plz tell me with formula its urgent...plzzz... and also tell me that this 40 amp at all phases mean 40 amp on red,40 amp on yellow,40 amp on blue...... or the total sum of that 3phase is 40 amp....

7 Answers  


we have provided 30 nos. relay contacts in panel.I want to know how do we do the numbering for the relay contacts as per any applicable standards

0 Answers  


why we not connect the 12 V batteries in parallel to get the more backup supply for an UPS ? wheter off line or on line UPS ?

2 Answers  


Even when a particular generator in a generating station is under maintenance we are still able to maintain the same power output. How is this possible? Does the tie line between 2 generating stations have a role to play in it?

1 Answers   NTPC,


What is the diffrence between an ELCB(earth leakage circuit breaker) and RCCB(residual current circuit breaker)?which has higher degree of safety and why?

2 Answers  


In zero voltage we can pass supply to our body means we cant get shock its true ? how we can do it ?

4 Answers  


How delta connection in the primary of distribution transformer reduces harmonics?how delta connections reduces harmonics?Please answer me...Hope that question is correct.

0 Answers  


low voltage grounding is done by?? 1)solidly gnd 2)ressistance 3)reactance

1 Answers  


What is the advisble power factor to be maintained in grid connecting power generation plnats without any effecting the generator.

1 Answers  


why electric shock due to dc is dangerous than that of ac

8 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)