1.In two wattmeter method if one wattmeter shows Negative
reading then wat is reason?
2.Wat is the reason for low voltage in houses?
3.Wat is meant by current and voltage? wat is difference
between the two?
Answers were Sorted based on User's Feedback
two watt meter method is used in measurement of power under un balanced condition.there are two reasons for - ve value
1). if load consist of more inductivd or capacive load with negligible resistive then it will show _ve value .pf angle is more than 65 deg
. in case of induction motor no load test one of the watt meter will indicate _ve because no load pf is 0.2 lag pf angle is nearer to 75 deg
2).reverse. connections of current coil
Is This Answer Correct ? | 98 Yes | 6 No |
Answer / max
1)hmm exacly opp
that means pf of load is less than 0.5 but greater than 0
2)load unbalance inductive load(?)
3)voltage -cause n current -effect
Is This Answer Correct ? | 49 Yes | 20 No |
Answer / sanjoy
5.Yes. It’s possible one wattmeter may indicate a negative value. One Wattmeter will read negative watts if the power factor goes below 0.5 .
Is This Answer Correct ? | 24 Yes | 4 No |
Answer / nitin banegaon
its sooo simlpe. when induction motor is on load then the no load current will have two components one is active/load component and other magnetizing component. Magnetizing component is for creating magnetic field to spin the motor which is independent of load current and it lags behind the voltage by 90. Initially on load, current is so small which is normally is in phase with applied voltage. So on no load circuit is inductive. So power factor is small nearly 0.2 to 0.4.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / syam kumar
2.reasion due to low voltage in houses is, in our street
poles we have generally 3 phase wires and 1 neutral
wire.every house connected to 1 phase and neutral wire.if
more number of houses connected by same phase then those
are effected from this low voltage problem.so some houses
will have power and some houses effected from this low
voltage. so if we connect equal distribution to all phases
this effect is reduced. this connection will given by our
linemen.
3.flow of charge is current
and potential difference between any two points in a
conductor is called voltage.
voltage and current are combinational.
Is This Answer Correct ? | 6 Yes | 4 No |
Answer / kd
1.power flow is in the reverse direction
2. Power factor is less than 0.5
Thanks !
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / james nyoro
1;phase angle is greater than 90 degrees cos 90=0 cos-in
=math error
2;reverse connection of current coil
Is This Answer Correct ? | 2 Yes | 7 No |
Answer / kaushik patel
But how measure it negative value. That is below in 0. And the pointer go to below zero and below zero not mention calibration then how measure it?
Is This Answer Correct ? | 0 Yes | 5 No |
Answer / vikas
because in wattmeter there r two internal winding i.e., m
and c which need to be short . if ther are not short then
one wattmeter shows negative value.
Is This Answer Correct ? | 5 Yes | 44 No |
Write the programming software name for LG, SIEMENS,Messung,AB
what will happen if dc is supplied in acb or mccb or other circuit breakers?
generally the electrical equipments not to be operated at leading power factor, why?
we have one oven for 12 zone we are installed ir lamp in oven we control load from thyrister and 0 to 5vdc so our zone no 8 getting bright in fraction of second so what we do.. Please answer
when we design electrical schemes of 11/.415kv distribution..wen and were should we show the relays??what is the function of it?for example..we place EFR Relay CT between transformer neutral link and transformer earth.Like this what are the other type of relays we should use?why?where?Explain please..Thank you
what is tandem isolator ??????????
what causes contact chatter when there is no demand on the air conditioning unit?
In 400KV Switchyard, we have used Circuit Breaker With PIR, what is the significance of PIR & why they'r used?
What is the dimension of A4 sheet in mm?
If a transformer primary winding operates at 240v, the secondary at 120v and the load is 1500w & the transformer is rated at 92% efficient, what's the current flowing through the primary winding of the transformer? What is the formula for finding this?
How do i carry out or know the vector group of a Dyn1 and Dyn5 transformer
What is time invariant system?