1. What means HART communicator / where it is used /
how to use it?
2. Types of Thermocouples and its temperature ranges /
output of thermocouple?
3. Types of RTDs and its temperature ranges / output
of RTD?
4. Idea about Temperature Transmitters?
5. Difference between Analog and Digital signals?
6. Difference between “2 wire” and “4 wire” system /
instruments?
7. Difference between “Potential” and “Potential free”
contact?
8. Types of flow meters / transmitters?
9. Types of level transmitters?
10. Difference between “Power/Control” cable
and “Instrument” cable?
11. What means “shield” and “screen” in cables / how it
is useful?
12. Draw a schematic of closed loop circuit of flow /
level / pressure / temperature?
13. Idea about calibration of Control valve /
positioned / I/P?
14. How to bypass a digital/analog signal in PLC/DCS by
hardwire and software?
Answers were Sorted based on User's Feedback
Answer / rajesh
1.HART is Communication Protocal.it is used to Communicate
the Field Instruments for measuring and Calibrating purpose
2.K Type : 0-1370 degrees
J Type: 0-700 degress
B Type: 200 -1800 deggress
R type: 200 - 2450 degrees
Output of Thermocouple is DC Potential (milli volts)
3.Platimum RTD :PT-100 Range:-270 to 600 degress
Output of RTD is Resistance
4.Temparaure tranmitters
it will receive the sinal from sensor (thermocouple /
RTD) and this signal will convets to 4-20mA or 0-20mA
5.Analog Signal is contioues measuring signal ie it's
measuring Range is 0 to 100%
Digital signal is a Binary form ie. Its state is Either
High (1) or Low(0)
6.in 4 wire Tranmitter Have Seperate exitation Supply is
for its Operation and Output taken for seperately.if the
Tranmitter Elecronic Cercuit is drawing More than 4 ma of
current then it will apply the 4 wire scheme.
in 2 wire Tranmitter working supply and its output is
taken in same cable.ie its working supply is lessthan 4 ma.
| Is This Answer Correct ? | 63 Yes | 6 No |
Answer / bm
Rajesh has answered 1st 6 qtns. The rest answeres are:
7. Potential contact means there will be a voltage in the
contact whereas potential free contact means that there
won't be any voltage in the contact. The user can take any
voltage basd on the contact rating in the pot free contact
to use further for his application i.e driving some
relay/contactor.
8. Types of flow meters: Rotameter, Venturi FM, Wedge FM,
Ultrasonic FM, Turbine FM, Magnetic FM, Vortex FM, Mass FM.
9. Types of LT: Displacer, GWR LT, Capacitance LT, DP LT,
FMCW LT, Ultrasonic LT.
10. Power/control cable has supply voltage of more than 24V
with no current signal, generally used to actuate
electrical contactors/solenoid valves.
Instrument cable is used to carry "mA" signals or potential
free signals.
11. shield / screen are same to avoid the noise in the pair
cables.
12. Not able to draw here.
| Is This Answer Correct ? | 32 Yes | 2 No |
Answer / nilesh karpe
Rajesh & BM has ansered 1 to 12 questions:
13.first check the stroke of the valve.ie. fully open &
then full close(for checking smooth operation).
ZERO CALLIBRATION:
at full close see the demand of i/p is 4MA.& output for
this is 0.2 KG/cm2. if not adjust through ZERO pot in i/p.
SPAN CALLLIBRATION:
fully open the valve.at this time the dmd of i/p should
20MA.at this time o/p supply air should 1KG/CM2.if not
adjust the span pot in i/p.
REPEAT THE ABOVE STEPS IN TILL ZERO & SPAN READINGS
MATCH.CHECHK INTERMIDIATE POSITIONS i.e. for dmd signal of
4,8,12,16& 20MA.FOR LINEARITY CHACKING.
| Is This Answer Correct ? | 23 Yes | 0 No |
Answer / manish kumar singh
Ans.1-
HART
The HART system (and its associated protocol) was originally developed by
Rosemount and is regarded as an open standard, available to all manufacturers. Its
main advantage is that it enables the retention of the existing 4-20mA
instrumentation cabling whilst using, simultaneously, the same wires to carry
digital information superimposed on the analog signal.
HART is a hybrid analog and digital system, as opposed to most field bus systems,
that are purely digital. It uses a Frequency Shift Keying (FSK) technique based on
the Bell 202 standard. Two individual frequencies of 1200 and 2200 Hz,
representing digits ‘1’ and ‘0’ respectively, are used. The average value of the
1200/2400Hz sine wave superimposed on
| Is This Answer Correct ? | 15 Yes | 1 No |
Answer / manish kumar singh
Ans.2- Type
Symbol Materials Temperature limits(°C)
S Pt10%Rh-Pt -50 / 1760
R Pt13%Rh-Pt -50 / 1760
B Pt30%Rh-Pt6%Rh 0 / 1820
E Cr - Co -270 / 1000
J Fe - Co -210 / 1200
K Cr - Al -270 / 1370
T Cu - Co -270 / 400
N Nicrosil-Nisil -270 / 400 (1) 0 /1300 (2)
W3 W3%Re- W25%Re 0 / 2310
W5 W5%Re - W26%Re 0 / 2310
| Is This Answer Correct ? | 9 Yes | 2 No |
suppose, after calibrating a transmitter we fixed it in a process line. At live zero condition the Tx shows 4.5 mA. what should we do to make the Tx show 4 mA? If we adjust zero, will it not affect the calibration?
what are the difference between conventional and smart transmitter.
What is the procedure of mounting new positioner on pneumatic control valve?
INtools Trainining
1 Answers Monarch Techno Engineering Solutions,
what is the diffrence between pressure safety valve & pressure relief valve....pls
WHEN DO WE GO FOR FMCW TYPE RADAR & PW TYPE RADAR ?
how to write the program for single push button by using ladder diagram
Define the difference between a stable versus an unstable controlled system and some of the tools you might use to be able to detect when this is happening and assumptions used for control system application design that could contribute to instability
I need circuit for RTD senser?
what is an ambient temperature?
What is the input impedence of an OPAMP as an ideal device.
how can we tune a PID. If it is by zeiger nichols method..please explain briefly with help of an example.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)