why are use only 4 to 20ma. signal.
Answers were Sorted based on User's Feedback
Answer / eswar
we are using 4 ma instead of 0 ma because the in order to
differentiate 0 input and fault condition(open circuit cable
or transmitter).
we are using maximum of 20ma because current above range can
cause fire or spark from short circuit conditions due to
weak installations.
| Is This Answer Correct ? | 56 Yes | 8 No |
Answer / abdus sattar mollah
initially,0-20ma of current is used as an transmitting
standard unless a objection was met.It was that:0 ma of
current used to indicate no signal/minimum signal from a
signal conditioner but if there is a faulty condition(such
as loop break),then also it will be show 0 ma of
current.Operator may think that there is no signal but
actually a fault has occured.So he cant distinguish between
them unless the plant is damaged.This is called TRUE ZERO.
So,after a reserach a new standard was proposed i.e 4-20 ma
of current.There was minimum interference in this
range,good quality transmittance,low power consumptions.So
this satndard is used.
| Is This Answer Correct ? | 37 Yes | 1 No |
Answer / deepesh
1) As stated earlier, 4mA is used to avoid the conflict
between live zero and dead zero.
2)In 4 mA to 20 mA range, current to pressure converter
gives linear output.
3)This range is intrinsically safe.
4)Low power consumptions
| Is This Answer Correct ? | 17 Yes | 2 No |
Answer / v.r.m.kiran
We are using 4 to 20ma because
1. Distinguish between process Zero & Instrument Zero.
2. It is easy to convert 4 to 20ma to 1 to 5v(Digital
Signal) by using a 250 Ohms Resistor in series.
V = IR
V=4*250=1000 MV = 1V, 8*250=2000 MV = 2V, 12*250=3000 MV =
3V, 16*250=4000 MV = 4V, 20*250=5000 MV = 5V.
3. Now we are using digital Indicators for display. Olden
days there will be analog display meter in the transmitter
for indication(0 to 100)%. When we apply 4ma or while
checking the transmitter online pointer should indicate
zero then we say that instrument is working correctly but
it comes bellow zero we have to check our instrument & have
to calibrate.
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / nagarajan audaiyarpatti
In the fault or open condition we cannot find the 0mA as 0
sothat the 4 mA consider as a zero and 20mA as a span ,in
this condition we can maintain 250mohms in the loop,sothat
we use usually 4 to 20 mA instead of 0 to 20mA in the
transmitter for measuring all the parameter such as
pressure ,temperature ,level,flow.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / sachin bijole
there is no required above current of 4 mA at zero % range b'cause of faulty condition we think the current have found 0 signal.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / hari
In industry we using 4 to 20 MA b'cuz drop of voltage will
less ...the signal will transmit long distance ..so sme
kind of drop voltage will there ..
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / mr gauge
We use 4mA instead of zero because 4mA is a minimum current
required to power up the transmitter, positioner etc. How do
we get the device turn on with no current.
| Is This Answer Correct ? | 7 Yes | 34 No |
in the flow caluclation k value how to caluclate.mass flow & volum flow.
Why 4ma - 20ma signal used in instrumentation??
Why Flow measure in Square-root?
can i calibrate DP transmitter online (while Tx in Service) if yes ,how?
Whether the DP transmitter can be utilised in the medium of Vaccum for the measurement of Level?
what is droop mode n frequency mode in wood ward governor?
With N nodes and B branches what will have a network ???
What is T4 temperature in compressor?
how to replace the smart transmitter software
In control valve there are two type of valve seat we can use metal to metal seat & soft seat.On this valve seat i have following doubt. 1)I have never seen practically the internal assembly of valve so my doubt is that basically weather the seat is soft seat or metal its basic MOC is same as valve body(SS or CS) only in soft seat we are using PTFE ring & place on valve seat & in metal this PTFE ring is not threr am i correct??????? 2)what are the common general rule for using metal to metal seat & soft seat,means its depend on process parameter like liquid,gas, steam & on valve leakage class.
hi sir yhis is zahid ali i am preparing for the jspl at oct.4.please send me the recently updated sample paper.
Draw a complete P&ID of a flow suction tank indicating all control & protection equipment. Indicate all its inlets and outlets. Explain the controls for this system
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)