What is the role of P(Protional), I(Integral) and D
(Derivative) in PID Controller?
Answers were Sorted based on User's Feedback
Answer / arulnainar
1.P(Proportional): to calculate the error signal (Error
signal means the difference between Process variable(PV)and
Setpoint.(E=SP-PV)-- Present(Howmuch)
2.I(Integral): to remove the offset error. It will decide
howlong the error exist in the cycle.(Iitegral time in RPM
or MPR)--Past(HowLong)
3.D(derivative): It will decide how fast the control action
to remove the error without any overshooting or
undershooting in the process for future cycle.
For practically we can say Howmuch(present), Howlong(Past),
Howfast(Future) respectively P,I,& D.
| Is This Answer Correct ? | 39 Yes | 2 No |
Answer / abdus sattar mollah
lets us dscribe the role of indivitual |P,|I,|D in |PID
controller....
|P(proportonal)==to give one to one correspondense between
the error signal and manipulated signal.This give linearity
between the above two signal and thus bring output varialbe
to controlled value or set point.
|I(integral)==to remove the offset error.
|D(derivative)==to fasten the control action.
| Is This Answer Correct ? | 10 Yes | 1 No |
P(proptional):To control the present difference between sp
and pv
I(integral): To control the past
D(derivative) :To control the futcher
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / arpan singhania
PID controller.....
P is to attain the set point..
I is to remove the offset error..
D is to make the action fast and controllable..
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / www.islamqa.com
Actually we can make it simple:
# P:
it's a controller gain which modify the controller o/p
proportional to the error.
# I:
it's a controller gain which modify the controller o/p
proportional to the integral of the error.
# D:
it's a controller gain which modify the controller o/p
proportional to error rate of change.
We have 4 parameters in our control loop to focus on:
1 - the rise time: the period of time during which the pv
get 90% of the desired sp value
2 - max overshoot
3 - settling time: the period of time during which the pv
get the desired sp value and saturate.
4 - error/offset
we can get it clear from this pic:
http://controls.ame.nd.edu/ame437/S2003/hw1/specifications.j
pg
Now we will take a look about the effect of each controller
gain on these parameters:
# P gain:
decrease rise time
increase max.overshoot
increase settling time
decrease error (but not eliminate)
# I gain:
decrease rise time
increase max.overshoot
increase settling time
eliminate error.
# D gain:
no effect on rise time
decrease max.overshoot
decrease settling time
decrease error.
the previous is guidelines to be in background while
dealing with PID,but they are not sharp limits.
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / panchal c.a.
Proportional- to control the offset between the process
variable and the set-point.
Integral- to control the time duration of the offset error.
Derivative- to control the rate of change of error.
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / praveen kumar
P- means Offset remains
I- means removes the offset
D- means fast action,
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / chandra mohan
in PID controller
P controller used for reducing the over shoot,
I-controller used for reducing the offset,
D-controller used for reducing the ossilations
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / praveen kumar
p--> directly proportional to the process variable and give final element to fast action
i--> responds the error between process variable and setpoint
d-->rate of change of error with respective time.
| Is This Answer Correct ? | 0 Yes | 0 No |
How d.p. Transmitter can be applied to close tank?
What is a flow meter?
A temperature sensor (RTD) connected via a temperature transmitter is adjusted to give an output of 4ma at 60 deg and 20 ma at 600 deg. This output (4-20ma) from the transmitter is connected to an IGBT-inverter to control a high speed (-12,000 to +12,000 RPM) DC motor. And in the inverter it is programmed as, for 4ma the motor speed will be -3,000 RPM and for 20ma the motor speed will be +10,000 RPM. The question is : If the motor speed is +5,500 (RPM), what will be the temperature? (-sign indicates that the motion is in reverse direction).
how to measure temperature from resistance of rtd?and how to measure temp from voltage of thermocouple?is there any formulas?
what is the importance of CV in the control valves? how it is calculated?
how to check control valve was passing?how to check online?
Please explain for RS 485 & RS 232 communication
How to Calibrate Vortex Flow transmitter in field
1. How can leveltrol be installed in steam drum for measuring the level of steam drum?
Define magnetic flow meter and mass flow meter.
Capacitance, resistance ( colour coding ), parallel & series circuits.
what is the difference between mmhg & mmwc?. i want to calibrate a transmitter in the range of -100 to 300 mmwc. Which is the reference for calibrate the Tx,if mmwc not available?. Is it mmhg or mmho2?.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)