Answer / carl_ellis
A loop folder is a manila folder or an electronic folder
that contains an assortment of documents related to the
instrumentation for a specific process control loop.
The exact contents of a loop folder are defined in a
project's standards/requirements.
A loop folder typically includes
- instrument manufacturer's spec/data sheet
- P&ID
- loop diagram
- loop check test sheet/checklist
- instrument calibration cert
- plot plan/location diagram
It can include
- loop test procedure
- hook-up diagram/instructions
- control/function narrative
- alarm setpoint list
- construction completion certificate
- interlock diagram
- flow sizing sheet
- CoC Certificate of Conformance
- COE Certificate of Origin
- MRT Material Test Report
- NACE certificate
- instrument configuration
(Compliments to Iris)
Carl Ellis
Measure First
| Is This Answer Correct ? | 36 Yes | 0 No |
What is DCS?
4 Answers GAIL, Sabic, Trident, Yokogawa,
Please can anybody tell me the step by step procedure for calibrating the Pr,Lvl,Fl,Temp transmitter on process?
what is cems analyzer explain with principle and drawing ?
SIR MAY I KNOW IF RADAR TYPE LEVEL TRANSMITTER SHOWING IN THE FIELD 0 % LEVEL AND IN DCS SHOWING 100% THEN WHAT IS THE CAUSE I CLEAN THE CHAMBER & TAKEN ONLINE BUT ONLY ONCE ITS BECOME ZERO IN DCS BUT AGAIN 100% SHOWING IN DCS,THEN I REMOVE THE POWER SUPLLY AND CONNECT IT AGAIN .IS IT OK BUT STILL IN THE DCS ITS 100% AND ON THE DISPLAY ITS INITILAZIATION PLEASE HELP ME READRING THIS?
what is the way of measuring air flow in air duct?explaim instruments used and DP creation in line?
what is the well head protection system?
WHAT IS THE DIFF BETWEEN FREQUENCY AND INTENSITY?HOW IT WORKS IN FLAME SCANNER ?
what is the zero and span trim?
1. what is modbus cable? 2. what kind of communication we are using for the interface of DCS, ESD and Third party cabinets? 3. What is serial communication and peer to peer communication?
when a magnet is heated?
A pressure transmitter with a range of 0-100 bar.The accuracy of the instrument is 1% of upper range value? The pressure indicating transmitter is showing the system pressure is 50 bar. b. When you include the error, what is the minimum possible pressure in our fuel gas system? i. 49.5 bar ii. 49 bar iii. 1 bar iv. 0.5 bar We want to change the filter cartridge. We must depressure the fuel gas system. c. After we depressure the system in preparation for maintenance, the transmitter displays a pressure of +0.1 bar. At this time, what is the possible range of pressures in our fuel system? i. +0.099 to +0.101 bar ii. 0 to +0.2 bar iii. -0.1 to +0.3 bar iv. -0.9 to +1.1 bar
If i have 4 Allen Bradely make RS logix 5000 PLC and for viewing that we are using 4 RS view SCADA for 4 different packages. Now, I will want to view two packages on only one SCADA. Then how i will do it?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)