What will be the full load current of 60KVA UPS. Suggest
for this formula.
Answers were Sorted based on User's Feedback
Answer / sujit288
60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps
So Full load current is 83 Amps.
Is This Answer Correct ? | 71 Yes | 8 No |
Answer / muralidhar k.s
Kw=1.732*V*Icos@
Kva=kw/cos@=1.732*V*I
I=1000/1.732*415
I=1.4*Kva
Full load current=KVA*1.4
The full load current for 60 Kva is 84amps.
Is This Answer Correct ? | 23 Yes | 1 No |
Answer / sreenu
Rating of UPS is in KVA, Hence it is just like a
transformer or alternator.
So I(Current)= S (Apperent power)/Voltage only.
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / guru
i agree with answar no 1.
we know,
W=v.i.cos@
therefore first converted kva to watt then calculate fl amp.
thank's sujit for appropriate....
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / murugesh.k
60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps
So Full load current is 83 Amps.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / kumar
formula of 3 phase power calculation
p=1.732*VL*IL*cos@
60*1000= 1.73*440*IL*0.9 (0.9 IS WE MAINTAIN POWER FACTOR)
IL=60000/685.87
IL=87 AMPS IN EACH PHASE THIS IS 100% LOAD DONT LOAD 100%
LOAD 80%ONLY MEANS 70AMPS
Is This Answer Correct ? | 9 Yes | 11 No |
Why Water motor is not taking a load or pressure while everything is correct. (Note: Motor running properly)
why transformer rating in kva ?
What is the main difference b/t Earth leakage relay & Earth fault relay.I want protect my LT panel(Distribution Panels)which relay have to propose.......
In a transformer, the hysteresis and eddy current losses depend upon 1.load current 2.maximum flux density in core 3.type of lamination 4.supply frequency The correct statements are (a) 1 and 3 (b) 2 and 3 (c) 1 and 4 (d) 2 and 4
what will happen reduce the transformer voltage from 415v to 406v, is it save the energy,? are this methodis good to reduce the energy.?
what you mean swtchgear(electrical)
why there is 1 phase and 3 phase but not 2 phase and 4 phase?
will we get shock from dc?
Why in ESP Positive earthed
why incomer bay is required before transformer bay if there are more than 1 nos. of transformer bay.
How can calculate the rating of a alternator for a given specific load with formula
0 Answers NRSC National Remote Sensing Centre,
what are the deffects for failure of PLC?