What will be the full load current of 60KVA UPS. Suggest
for this formula.
Answers were Sorted based on User's Feedback
Answer / sujit288
60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps
So Full load current is 83 Amps.
| Is This Answer Correct ? | 71 Yes | 8 No |
Answer / muralidhar k.s
Kw=1.732*V*Icos@
Kva=kw/cos@=1.732*V*I
I=1000/1.732*415
I=1.4*Kva
Full load current=KVA*1.4
The full load current for 60 Kva is 84amps.
| Is This Answer Correct ? | 23 Yes | 1 No |
Answer / sreenu
Rating of UPS is in KVA, Hence it is just like a
transformer or alternator.
So I(Current)= S (Apperent power)/Voltage only.
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / guru
i agree with answar no 1.
we know,
W=v.i.cos@
therefore first converted kva to watt then calculate fl amp.
thank's sujit for appropriate....
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / murugesh.k
60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps
So Full load current is 83 Amps.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / kumar
formula of 3 phase power calculation
p=1.732*VL*IL*cos@
60*1000= 1.73*440*IL*0.9 (0.9 IS WE MAINTAIN POWER FACTOR)
IL=60000/685.87
IL=87 AMPS IN EACH PHASE THIS IS 100% LOAD DONT LOAD 100%
LOAD 80%ONLY MEANS 70AMPS
| Is This Answer Correct ? | 9 Yes | 11 No |
If current flows through conductor it produce magnetic field only.but if current flows through vaccum both magnetic & electrical field produce why ?
What is the effect of interchanging core(made of steel) and winding(made of copper) material in case of transformer? Give proper explanation in regard to different losses in transformer.
Which modulation has higher data rates a.fm b.am c.qam d.qpsk
please I wont know how to calculate the vector group for power transformer ZNyn11 best regard.
my name is venkat .i have good percentage in my academics(ssc 86, intermediate 83 b.tech 73) my question 1..after completion of my ssc i joined in bpc but i didnt got rank in emcet so i completed MPC in one year compartmentally ..so here what am expect question from this background?
what is the difference between general inverter and solor inverter clerly explain plz
How the output,losses and temperature of machines varies with linear dimension?
how to select the power contactor in Diffrent AC motors.
in small capacitor we use uf( micro farad) and in big quantity we used kvar. i want to know that in 1 kva how much will b uf(micru farad).
Why dnt we generate 5-ph or 7-ph supply like as 3-ph supply
For a Potential Transformer(PT), the primary neutral terminal must be grounded before energization. Why....? What will be heppend if we energize the PT without grounded the primary neutral point? Why..........?
Why we are use 11KV / 22KV / 33KV / 66KV / 110KV / 230KV / 440KV this type of ratio. why cant we use other voltage ratio like 54KV / 99KV et.,
8 Answers College School Exams Tests, Hino, ITC Infotech, Reliance, UPRVUNL,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)