Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What will be the full load current of 60KVA UPS. Suggest
for this formula.

Answers were Sorted based on User's Feedback



What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / sujit288

60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps

So Full load current is 83 Amps.

Is This Answer Correct ?    71 Yes 8 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / muralidhar k.s

Kw=1.732*V*Icos@
Kva=kw/cos@=1.732*V*I
I=1000/1.732*415
I=1.4*Kva

Full load current=KVA*1.4
The full load current for 60 Kva is 84amps.

Is This Answer Correct ?    23 Yes 1 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / sreenu

Rating of UPS is in KVA, Hence it is just like a
transformer or alternator.

So I(Current)= S (Apperent power)/Voltage only.

Is This Answer Correct ?    5 Yes 3 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / guru

i agree with answar no 1.
we know,
W=v.i.cos@
therefore first converted kva to watt then calculate fl amp.
thank's sujit for appropriate....

Is This Answer Correct ?    3 Yes 1 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / murugesh.k

60kva x 0.8=48kw or 48000watt
we know p=1.732xVIcos@
I=p/1.732xVcos@
I=48000/1.732 X 415v X 0.8(Where V=415v)
I=48000/575
I=83Amps

So Full load current is 83 Amps.

Is This Answer Correct ?    4 Yes 2 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / sathishbabu t

p=v*i*cos

Is This Answer Correct ?    3 Yes 3 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / rahul

Full load current =Kva*1000 /v*Powe factor

Is This Answer Correct ?    0 Yes 1 No

What will be the full load current of 60KVA UPS. Suggest for this formula...

Answer / kumar

formula of 3 phase power calculation

p=1.732*VL*IL*cos@

60*1000= 1.73*440*IL*0.9 (0.9 IS WE MAINTAIN POWER FACTOR)
IL=60000/685.87
IL=87 AMPS IN EACH PHASE THIS IS 100% LOAD DONT LOAD 100%
LOAD 80%ONLY MEANS 70AMPS

Is This Answer Correct ?    9 Yes 11 No

Post New Answer

More Electrical Engineering Interview Questions

If current flows through conductor it produce magnetic field only.but if current flows through vaccum both magnetic & electrical field produce why ?

4 Answers   NTPC,


What is the effect of interchanging core(made of steel) and winding(made of copper) material in case of transformer? Give proper explanation in regard to different losses in transformer.

0 Answers  


Which modulation has higher data rates a.fm b.am c.qam d.qpsk

1 Answers   NTDC,


please I wont know how to calculate the vector group for power transformer ZNyn11 best regard.

0 Answers   Al Rasikh,


my name is venkat .i have good percentage in my academics(ssc 86, intermediate 83 b.tech 73) my question 1..after completion of my ssc i joined in bpc but i didnt got rank in emcet so i completed MPC in one year compartmentally ..so here what am expect question from this background?

0 Answers  


what is the difference between general inverter and solor inverter clerly explain plz

0 Answers  


How the output,losses and temperature of machines varies with linear dimension?

1 Answers  


how to select the power contactor in Diffrent AC motors.

6 Answers   Titan,


in small capacitor we use uf( micro farad) and in big quantity we used kvar. i want to know that in 1 kva how much will b uf(micru farad).

2 Answers  


Why dnt we generate 5-ph or 7-ph supply like as 3-ph supply

2 Answers  


For a Potential Transformer(PT), the primary neutral terminal must be grounded before energization. Why....? What will be heppend if we energize the PT without grounded the primary neutral point? Why..........?

2 Answers  


Why we are use 11KV / 22KV / 33KV / 66KV / 110KV / 230KV / 440KV this type of ratio. why cant we use other voltage ratio like 54KV / 99KV et.,

8 Answers   College School Exams Tests, Hino, ITC Infotech, Reliance, UPRVUNL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)