Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


When we change the tap position of 10MVA transformer it
suddenly tripped with Out of step indication and also with
Static differential relay indication, Transformer Bucholz
relay indn and Low oil level indication. Before 1 week the
same problem occured by changing the tap position. but at
that time only oltc bucholz relay activated. After testing
the TxR Relay team & PET team cant find any solid reason.
The values are ok also. So plz answer wat's the reason for
this incident? anybody plz help.

Answers were Sorted based on User's Feedback



When we change the tap position of 10MVA transformer it suddenly tripped with Out of step indicatio..

Answer / k.prakashchandra

OLTC has contact switches on rotating spindle and diverter
switch. Bucholtz relay acts as the oil is burnt in the
chamber due to arcing caused by loose contact .The spring
tension of the switches are to be checked for correct
tightness.If the contact is not correct ,the differential
relay may also act due to imbalance of currents.Do not
operate OLTC till the fault is set right.And the oil may
have to reconditioned.

Is This Answer Correct ?    2 Yes 0 No

When we change the tap position of 10MVA transformer it suddenly tripped with Out of step indicatio..

Answer / k.prakashchandra

There is a loose connection in one of the phases of OLTC
contacts.

Is This Answer Correct ?    0 Yes 0 No

When we change the tap position of 10MVA transformer it suddenly tripped with Out of step indicatio..

Answer / priyanka

Problem seems to be around the OLTC. More than 70% of
problems in transformer are due to OLTC.
Get your OLTC motor checked,surely you can find the
tripping reason there. Now about the tripping indications
following is the possibility-
Out of step - OLTC is a kind of stepper motor, when you
change the tap position the motor moves at a particular
step angle. In case your motor is faulty, it will move out
of step leading to frequent sparking across contacts
(Buccholz indication) and current imbalance due to improper
step angle (static differential).
Low oil level indication has no link with this, it simply
shows that conservator level is down.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

ROC converges if poles and zeros lie inside a. Origion b. Z=1

0 Answers  


what is differential relay in power transformer??

8 Answers  


what is the highest transmission voltage in india???

49 Answers   Bhel, EIPL, Engineering, Jindal,


We know that, in case if there is a faulty insulation,or sc, the current is bypassed to earth through the earth wire that has low resistance.Actually, what will happen to that current that flows through gnd?In that case,if we come in contact with that faulty appliance, wont that current flow through us as we form a closed path by standing in gnd?Is grounding a safety measure?

3 Answers  


WHAT IS RMU AND WHAT IS ITS FUNCTION AND HOW TODISCONNECT

3 Answers   Bhel,


When i went to a interview the interviewer ask me a question for that i cant able to answer him if anyone knows answer me How will you design a capacitor bank for a plant? if my p.f is 0.6 i have to improve it to 0.9 or 1 what kind of steps i have to do? and is there any formula for calculating this?

2 Answers  


what is form factor.and rms value..

1 Answers   IIM, Torrent Power,


how can calculated the rating of the 11 KV transformer?

6 Answers   NBCC,


Motor also having losses, we call KW rating. In transformer and generator having losses but we call KVA Rating why?

9 Answers  


can we use inductor for passing or blocking of AC or DC?

3 Answers   Moser Baer, NTPC,


Why the earth cable have current 1A - 2A , it is safety for Electrical system or earth cable should be zero amps ? how to troubleshoot?

0 Answers  


we have one oven for 12 zone we are installed ir lamp in oven we control load from thyrister and 0 to 5vdc so our zone no 8 getting bright in fraction of second so what we do.. Please answer

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)