When we change the tap position of 10MVA transformer it
suddenly tripped with Out of step indication and also with
Static differential relay indication, Transformer Bucholz
relay indn and Low oil level indication. Before 1 week the
same problem occured by changing the tap position. but at
that time only oltc bucholz relay activated. After testing
the TxR Relay team & PET team cant find any solid reason.
The values are ok also. So plz answer wat's the reason for
this incident? anybody plz help.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
OLTC has contact switches on rotating spindle and diverter
switch. Bucholtz relay acts as the oil is burnt in the
chamber due to arcing caused by loose contact .The spring
tension of the switches are to be checked for correct
tightness.If the contact is not correct ,the differential
relay may also act due to imbalance of currents.Do not
operate OLTC till the fault is set right.And the oil may
have to reconditioned.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
There is a loose connection in one of the phases of OLTC
contacts.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / priyanka
Problem seems to be around the OLTC. More than 70% of
problems in transformer are due to OLTC.
Get your OLTC motor checked,surely you can find the
tripping reason there. Now about the tripping indications
following is the possibility-
Out of step - OLTC is a kind of stepper motor, when you
change the tap position the motor moves at a particular
step angle. In case your motor is faulty, it will move out
of step leading to frequent sparking across contacts
(Buccholz indication) and current imbalance due to improper
step angle (static differential).
Low oil level indication has no link with this, it simply
shows that conservator level is down.
Is This Answer Correct ? | 0 Yes | 0 No |
How to select the releases for MCCB ?
WHEN TWO ALTERNATORS ARE OPERATING IN PARALLEL, EXPLAIN WHY IT IS OBJECTIONABLE TO OPERATE ONE AT A LEADING POWER FACTOR AND ONE AT THE Lagging power factor?
what is high pot test on 11kv switchgear and how to apply high voltage on panel what is spheare gap and how to determine its celeberation.
how electrical energy is converted into mechanical energy in dc motor
Which companies are into the project management of construction of power transmission line?
Why the suply frequency in INDIA is 50HZ
Why do power lines not short out when they fall into water?
Write down the brushes of a de machine.
How do you connect the capacitors on polyphase circuits?
What is the function of a capaitor in 1-phase IM?
what are the specifications we must look at to select a relay for any capacity motor?
in 3 phase (4 wire) star connection - is current pass through neutral??