why the transformer ratings in kva or mva?
Answers were Sorted based on User's Feedback
Answer / murali290
For any device the rating is given based on the losses occur
in it (loss is nothing but heat).In transformer 2 types of
losses occur 1.core losses: which depends on V &
2.cu losses: which depends on I only
but no losses depends on p.f.
therefore trasformer rating proportional to VI or VA
for large transformers the rating in kilo or mega ,hence
KVA or MVA
Is This Answer Correct ? | 13 Yes | 3 No |
Answer / m.anand
copper loss and iron loss depends only on current and
voltage there is no phase angle involved in between voltage
and current.so powerfactor is not factor affecting
transformer rating ...
hence transformer ratings are in KVA
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / jd
Since we don't know the type of load that the transformer would be bearing in future. thus the manufacturer specifies its rating in KVA or MVA
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / gopalakrishna
transformer ratting are always in KVA or MVA why because
transformer iron losses are depen upon current, and copper
losses are depending upon voltage hence the rattings of the
trans former rattings are in 'kva'
Is This Answer Correct ? | 3 Yes | 4 No |
Why the brushes used in dc machines are made of carbon not from other metal?
what happen when increase or decrease size of lamp,light.glass.
ynchronous M/C with under excitation with reactive power absorption , acts as a) synch. Motor b) synch gen c) synchr capacit
Why do we generate 3 Phase AC Supply? It is possible to generate 4 Phase and 5 Phase explain it?
How to calculate busbar size & what is the procedure we make for determine that?
35 Answers Auko Tex, Integra, PowerTech, Shadhin Group,
Is it possible to connect a dYN1 transformer in parallel with a YNd11 transformer.
What should be distance required in between two phase of HT cionductors in open area??????
For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply was applied at the HV. Connection between Aa was made with a 2.5mm cable. As soon as power was switched on the cable caught fire and burnt. This test was then abandoned. It is noteworthy to say that a similar cable was also used in a similar transformer for the same. The cable did not burn and test was successfully completed with good result. What is wrong? Please, help me out.
why Transformer and DG rating capacity is in KVA
Why P.F(power factor)relay should not be connected to the D.G(diesel generator) incomer side
How we can change the direction of rotation of Induction motor? Prove it using graphical