what is the difference between neutral and earth
Answers were Sorted based on User's Feedback
Answer / pravesh
the main difference between the earth and neutral is that
the neutral is connected to the circuit and work as the
return path for the circuit , but earth works as for
protection of the appliences , if any leakage current
exists in the circuit earth conductors work at zero
potential and gives low resistence path to the leakage
current
| Is This Answer Correct ? | 63 Yes | 2 No |
though neutral and earth may look to serve same purpose but
neutral is a part of circuit,it allowes return path for
current,it has many advantages,a neutral is used in 3phase
transformer to reduce harmonics &makes secondary output
fairly sinusoidal,on the other hand earthing means to
connect an electrical system to ground potential for
protection purpose,if any leakage current exists in
circuit, earthing forms a low resistance path to ground and
protect the operetor from electric schock.
| Is This Answer Correct ? | 25 Yes | 0 No |
Answer / naveen
neutral is the return path and ground carries only fault
current.
| Is This Answer Correct ? | 14 Yes | 3 No |
Answer / antwan mojito
The primary difference between neutral and earth is safety.
Although both eventually terminate to earth they have
seperate functions. Using an electric drill as an example.
Neutrals provide a closed circuit, or path, which allows
the drill to function. The earth ground is provided in case
of a short inside the drill. The electricity will go
through the earth ground instead of the person using the
drill, preventing injury or death. Anyone old enough can
remember the old 2-prong wall outlets. The earth ground
safety is why we now use 3-prong outlets.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / tse-wang
Electrically Neutral is different from Eaarth.
Neutral is (assumed) electrically zero potential point and
if any line (wire) is connected between the neutrals it's
function is just to balance the current in two or many
circuits.
Earth is a system designed and connected to the electrical
appliences to bring the connected point (appliences) to
electrically to the earth level (which we assume to be
zero). To be specific, the earth potential is not always
zero. However, connecting the earth (our standing point or
the next touch point electrically)to the electrical
appliance will try to ballance the two connected points to
equi-potential (same voltage level) level. and avoid flow
of current through. That's why earth connection should be
made by low resistant wire.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / tenon
Neutra: Neutral is Retern Path.
Eartth: Earth is Seafty device.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / ashok mishra
earthing is connected to earth
earthing is at zero potential and its just for saftey of equipment and operator
nutral is the central point of star connection and used to complete the circuit
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / md. obaydur rahman
Since the neutral point of an electrical supply system is
often connected to earth ground, ground and neutral are
closely related. Under certain conditions, a conductor used
to connect to a system neutral is also used for grounding
(earthing) of equipment and structures. Current carried on a
grounding conductor can result in objectionable or dangerous
voltages appearing on equipment enclosures, so the
installation of grounding conductors and neutral conductors
is carefully defined in electrical regulations. Where a
neutral conductor is used also to connect equipment
enclosures to earth, care must be taken that the neutral
conductor never rises to a high voltage with respect to
local ground
| Is This Answer Correct ? | 0 Yes | 0 No |
Why lose 1 phase voltage in 33kv to 415v stepdown transformer
Why voltge arev transformed in to 132KV/66/KV/33KV like that
At no load the PF of an alternator -Zero -Zero Lagging -Zero leading -None of the above
Advantage of LT panel vs HT panel
why in a swquence network representation, the negetive sequence generated voltage is taken as zero?
if current required for triggering thyristor at -30 degrees(temp) is 80 mA, what is the current required at 60 degrees
11 kv input, 66 kv input advantages
For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply was applied at the HV. Connection between Aa was made with a 2.5mm cable. As soon as power was switched on the cable caught fire and burnt. This test was then abandoned. It is noteworthy to say that a similar cable was also used in a similar transformer for the same. The cable did not burn and test was successfully completed with good result. What is wrong? Please, help me out.
why two wires are wound alternately to each other in single phase wires?
in a delta-star with neutral grounding on star side what will happen if one star limb got opened at star point
Why is it prefer to initiate circuit breaker failure by "86" lockout relay not by "94" tripping relay ?!
what is meant by LCR meter? where its useful ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)