what is PI value and its significance for insulation
testing?
Answers were Sorted based on User's Feedback
Answer / biju9cr
Knowing the polarization Index of a motor or generator can
be useful in appraising the fitness of the machine for
service. The index is calculated from measurements of the
winding insulation resistance.
Before measuring the insulation resistance, remove all
external connections to the machine and completely discharge
the windings to the grounded machine frame.
Proceed by applying either 500 or 1000 volts dc between the
winding and ground using a direct-indicating, power-driven
megohmmeter. For machines rated 500 volts and over, the
higher value is used. The voltage is applied for 10 minutes
and kept constant for the duration of the test.
The polarization index is calculated as the ratio of the
10-minute to the 1-minute value of the insulation
resistance, measured consecutively.
Polarization Index =
Resistance after 10 minutes/
Resistance after 1 minute
The recommended minimum value of polarization index for ac
and dc motors and generators is 2.0. Machines having
windings with a lower index are less likely to be suited for
operation.
The polarization index is useful in evaluating windings for:
* Buildup of dirt or moisture.
* Gradual deterioration of the insulation (by comparing
results of tests made earlier on the same machine).
* Fitness for overpotential tests.
* Suitability for operation.
| Is This Answer Correct ? | 46 Yes | 4 No |
Answer / mohammed sarfraz
POLARIZATION INDEX is ability of the insulation to absorb
the voltage over a period af time, this give an indication
of the overall insulation quality of individual pieces of
insulation in the transformer. this test is usually
performed as ratio of insulation resistance for 10 minutes
to ir value of 1 minutes.
the value should be less then 2.5.
| Is This Answer Correct ? | 35 Yes | 27 No |
Answer / maheshwar prasad
Polarisation index is the ratio of megger value taken for 10 minutes to the megger value taken for 1 minute. The significance of polarization index test. Let I be the total initial current during polarisation index test or PI test. IC is the capacitive current. IR is resistive or conductive current. IS is surface leakage current. IP is polarization current of the insulator. Value of insulation resistance test or IR value test, i.e. value megger reading just after 1 minute of the test, is- Megger value of 10 minute test, is Therefore, result of polarization index test, is From the above equation it is clear that, if the value of (IR + IS) >> IP, the PI of insulator approaches to 1. And large IR or IS or both indicate unhealthiness of the insulation. Th value of PI becomes high if (IR + IS) is very small compared to IP. This equation indicates that high polarization index of an insulator implies healthiness of insulator. For good insulator resistive leakage current IR is very tiny. It is always desired to have polarisation index of an electrical insulator more than 2. It is hazardous to have polarisation index less than 1.5.
| Is This Answer Correct ? | 2 Yes | 0 No |
how to reduce the transformer size in ups ?
sir what is the purpose of SF6 in HT breaker and what is the pressure should be maintain in the breaker?
I have a one P.F meter in my factory showing 2 phase leading and one phase lagging then what is my actual P.F.
what is load cell
Differentiate between kirchhoff’s first law and kirchhoff’s second law?
can i use 4 number of circuit breaker as single phase manual change over switch? if yes then how plz also send ckt diagram at nazimzamurad@gmail.com
why we are using DC supply for all protection relays, why cant we use AC supply..???
How each of the following losses occur in d.c machines (i) copper (2)core (3) windage (4)friction please help me
A 500 V shunt motor runs at its normal speed of 250rpm when the armature current is 200A. The resistance of the armature is 0.12 Ω. Calculate the speed when a resistance is inserted in the field reducing the shunt field to 80% of normal value and the armature current is 100A.
what is IDMT relay.
if 300 hrs not comleted at wat interval b.c,d checks og take place
what are the types of starter ?
25 Answers Andhra Sugars, Bhel, Eveready, HyFun Foods, Jindal, ME, Valeo Lighting Systems India Private Limited,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)