I have a one P.F meter in my factory showing 2 phase leading and one phase lagging then what is my actual P.F.
Answer / abdullah al baki
You can do it in 2 ways. 1. You can connect a 3-phase P.F meter and see the reading directly. OR 2. You can measure the P & Q by using watt and VAR meter per phase and add them in complex (phasor) form to get the total P.F.
| Is This Answer Correct ? | 0 Yes | 0 No |
Do you know how to measure the earth resistance?
Explain Even and Odd signals?
Why IR value of the (HT cable Plus synchronous motor) is less while individually having IR values in GΩ?
Why there is not any reactive power in DC although it causes magnetic field.
we have one ups its neutral is not earthed.its one distribution MCB has a earth fault.but we can not put off any MCB.so how to find out that in which circuit is earthed without isolating the breaker.
what is difference between fuse and breaker?
Seamless tubes are made by?
How much ampere rating on LT side of distribution transformer and also on HT side of 200KVA transformer
how to measure earth pit resistance
7 Answers BARC, BYD Electronic, Construction,
What id difference between power and energy?
what r the safety measures in UPS ? explain all?
for 8 mva 33/11 kv transformer what will be the setting of differential relay on which it trip & what is the HF setting in this relay
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)