Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


formula for cable size calculation for current?

Answers were Sorted based on User's Feedback



formula for cable size calculation for current?..

Answer / govardhana rao.p

Calculations are same as above but for 50A load

We can use the bellow cables

Aluminium: 50 x 3.5 Core

Cu : 16 x 4 Core

Is This Answer Correct ?    115 Yes 61 No

formula for cable size calculation for current?..

Answer / sabu

in case 50amps 230v single phase load we can use 16mm aluminium and 10mm copper

Is This Answer Correct ?    29 Yes 6 No

formula for cable size calculation for current?..

Answer / zafar

the answer is not correct the correct figure is 25mmsq

Is This Answer Correct ?    37 Yes 19 No

formula for cable size calculation for current?..

Answer / bipin naik

The current will be 27 A for single phase supply(230v)

Is This Answer Correct ?    4 Yes 0 No

formula for cable size calculation for current?..

Answer / fathi

2x10 sqmm Cu/XLPE/PVC 600/1000 v

Is This Answer Correct ?    17 Yes 16 No

formula for cable size calculation for current?..

Answer / engr.muhammad younas khan

SINGLE PHASE FORMULA FOR CABLE SIZING.

REQUIRED DATA:-
I :- AMPERES
L :- LENGTH OF CABLE.
K :- CONDUCTIVITY OF COPPER(58)
:- CONDUCTIVITY OF ALUMINUM (36)
Vd:- VOLTAGE DROP.

GIVEN DATA:
I:- 50 AMPERES.
L:- 100 METERS.
Vd:- 3% ACCEPTABLE OF 230 VOLTS

FORMULA:-
AREA (mm2)= 2*I*L/(K*Vd)
= 2*50*100/(58*6.9)
= 24.98 mm2
= ALMOST 25 mm2
FOR THREE PHASE:
AREA(mm2) = 1.732*50*100/(58*12)
= 12.44 mm2
= ALMOST 15 mm2
3% voltage drop of 400 volts =12 volts.

ABOVE EXPLAINED FOR IS PROPERLT CORRECT.USE AND ENJOY.

ENGR.MUHAMMAD YOUNAS KHAN
M.SC.ENGG.MIEE(UK)
WAZIRABAD CITY,PUNJAB, PAKISTAN
DATE:- 24/3/2014

Is This Answer Correct ?    2 Yes 2 No

formula for cable size calculation for current?..

Answer / selvakumar

230 meter cable

Is This Answer Correct ?    2 Yes 3 No

formula for cable size calculation for current?..

Answer / lorp soophan

S=(2.l.i.cosg)/V%

Is This Answer Correct ?    0 Yes 4 No

formula for cable size calculation for current?..

Answer / vinay katoch

formula is same but for 50 amp load we can use 3.5c
25mmseq.all.and 10mm seq.cu.

Is This Answer Correct ?    18 Yes 28 No

formula for cable size calculation for current?..

Answer / gurunadharaov

by the formula p=v*i*cos@
assume the load as 5kw and operating at 230v and also
assume the load as inductive (so the power factor is 0.5
pf lag)


now by formula
5000=230*i*0.5
i=50A
NOW CABLE SIZE MUST BE > LOAD
SO CABLE SIZE IZ 65SQMM(ITZ DSSEPEND ON AL/CU CABLE)

Is This Answer Correct ?    118 Yes 136 No

Post New Answer

More Electrical Engineering Interview Questions

what is the working principle of ceiling fan and table fan?

10 Answers   ABC, Tata Steel Limited,


How should i design a 1ph & 3 ph transformer. Kindly let meknow all steps and formulaes related to design from scratch.

0 Answers  


what is the difference between earth, neutral and ground?

1 Answers   Farnek, Shyam Indus Power, Spiro Solutions,


What is the difference between UPS & inverter ? which UPS is better and whos got the edge ? what is the difference between & inverter ? which UPS is better and whos got the edge 12 V , 24 V , 36 V etc what are the advantages of 12 V, 24 V , 36 V etc and what are the disadvantages of 12 V, 24 V, 36 V etc thanks

0 Answers  


what is ground clearence ,what is minimum ground clearence ,i.e present value following in india ,is it changes wit conductor size ,kva rating.surface

3 Answers  


what mean by analog ,digital,numerical meters and relays? say the example?

0 Answers   ABB,


While connecting bulb in Series/Parallel,there is any difference in glowing

3 Answers  


List of equipments required foe industrial repair lab.

0 Answers  


Which Current transformer will be bigger in size, 400/5 or 400/1 & why?

2 Answers   Apollo,


WHAT IS THE MEANING CREEPAGE DISTANCE

1 Answers  


whati s the sludge current in ups

0 Answers   Future Group,


How to take of Transformer oil Break down voltage test?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)