Answer / amit upadhyay dscl
Step down transformer which is 11kv/415v.
| Is This Answer Correct ? | 32 Yes | 4 No |
Answer / sunil kumar
Step down as well as Delta star is must in distribution of
transformer
| Is This Answer Correct ? | 18 Yes | 1 No |
Answer / nibel
actualy the transformer we use in distribution side called
distribution transformer, 11kv/433v but depending upon the
impedence voltage ,regulation, primary voltage, load and
tapping positions the secondary voltage may vary. but we
maintain secondary voltage to 415v coz almost all electrical
equipments are designed for that voltage. normaly the
winding will be delta star.
the type of transformer depend upon costumer requirement,
oil cooled or air cooled. indoor or outdoor lik that.
| Is This Answer Correct ? | 2 Yes | 0 No |
Step down transformer which is 11kv/415v. Delta star conncetion
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mahmoud aboelfadel
distribution transformer is often 11kv/0.4 kv but the very important thing in this type of transformers is iron losses is least we can
| Is This Answer Correct ? | 0 Yes | 0 No |
what is dyn 11
WHAT IS SHORT CIRCUIT STRENGTH OF 100 AMPS MCCB?
what would happen if u assume to insulate all the overhead lines and no insulators....??do you think it to b an advantag or a disadvantage??justify.
KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these transformer has big size? Give reason
A resistor,inductor and capacitor are connected in series respectively.Voltage across resistor is 40v,across inductor is 70v,across capacitor is 100v.Then what is the total voltage applied across the elements?
what is the transformer
HOW TO CALCULATE LV CABLE SIZING?
I find that underground strip-armoiured,4core,LT PVC cables in an earthed power distribution sytem are occasionly found in charred condition-with no trace of it except ash. Is this because of no proper earth connection/continuity (giving rising to high armour resistance)in the joint enroute or because of insufficient capability (again due to high armour resistance)of cable-armour to carry fault current or due to neglected /unprotected overloading of the cable or due to high armour currents caused by power thefts where only phase(s) are unauthorisely tapped & at the point of poer consumption earth terminal is established by burring underground a not so good earthing rod (or using an underground water pipe for the purpose)
What is meant by reverse polarity and how it can be fixed?
in thermal power plants by opening the turbine governor valve increase the generator load. how
why the under of transformer platform is filled with rock stones.
10 Answers TNEB Tamil Nadu Electricity Board,
How to findout raw or ups power? its not indicated in socket,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)