What is the effect of leading power factor for power transformer & D.G?..

Answer / rabi

The stability of a generator depends on the field strength
of the magnetic field establishing in the air gap by the
rotor ampere turn. if the field is weakened the stability
margin is reduced.
Leading power factor causes field mmf (fm) to reduce and
rotor angle to increase towards 90 degree, the theoretical
operation of stable generation operation. Therefore a
machine operates well within its stability limit factor
with lagging power factor.
Transformer operation does not depend on power factor. For
that reason it is rated in KVA.

Is This Answer Correct ?    25 Yes 6 No

What is the effect of leading power factor for power transformer & D.G?..

Answer / om prakash

Leading power factor makes the current leading the voltage
it does not affect the transofmer but it affects the
D.G./Power generation unit. As for the power generation we
need to excite the excitor field which take the sensing
reference voltage from the output line of the generator.In
case of leading power factor the voltage will not dip on
increasing the load and hence the AVR will not be able to
excite the system properly.

Is This Answer Correct ?    20 Yes 4 No

What is the effect of leading power factor for power transformer & D.G?..

Answer / deepak chander

The transformer opration does not depends on the pf. The
major problem in leading pf is related to generation.
Stator end region heating depends on the pf. In leading pf
the altenator run at underexited operation and there is the
scope for flux to increase even over the saturation limit
of core. That causes the core heating on end region.

Is This Answer Correct ?    2 Yes 2 No

What is the effect of leading power factor for power transformer & D.G?..

Answer / ramesh kumar gupta

Leading power factor does affect the power Xmer within its
VA rating but it affects the D.G./a Generator unit.Due to
leading power factor the source excitation system runs in
under excited state and the deficit in excitation has to be
supplied by stator.Owing to this stator end core heating
problem observed.

Is This Answer Correct ?    1 Yes 3 No

What is the effect of leading power factor for power transformer & D.G?..

Answer / suresh

Leading power factor, means making Cos factor nearer to 1,
hence doing so you can achive the following,
1.partial reduction in load current hence losess get reduced
2.Efficency increases

Is This Answer Correct ?    5 Yes 13 No

What is the effect of leading power factor for power transformer & D.G?..

Answer / shaan

SHAAN FROM MADURAI:

LEADING POWER FACTOR IN TRANSFORMER THERE ARE REDUCE
INDUCTIVE LOADS

Is This Answer Correct ?    3 Yes 11 No

What is the effect of leading power factor for power transformer & D.G?..

Answer / guest

Leading power factor causes the the current to reduce,due to
which the generator gets overloaded at its full load capacity.

Is This Answer Correct ?    5 Yes 34 No

Post New Answer

More Electrical Engineering Interview Questions

Weather power factor correction needed for synchronous motors?

1 Answers  


if we have 320KVA Genset kindly advice how much load we can put it.

0 Answers  


why do harmonics generata?

1 Answers  


how the speed decreases of a generator in power station if load increases

1 Answers   Tata Power,


Q2). When 3 dice are simultaneously thrown, which of the following would be obtained? (a) Result 1: “A 5, a 3 and a 6” (b) Result 2:” A 5 three times” (c) Result 3:”A 5 twice and a 3” (d) All three results are equally likely. (Musigma Question)

2 Answers   Mu Sigma,






will a fluorescent bulb work when dc is passed through it?? if not why??

4 Answers   TCS,


On a 3 winding transformer YNynd11, how do you apply REF protection to the Delta tertiary winding that is supplying auxiliaries to a substation?

0 Answers   Kwekwe Polytechnic,


How we can calculate the consumption in kwh of motor on basis of kw @100% load, @50% load & @ no load.

0 Answers   Grasim,


What is the unit of inertia constant of rotating machines? Which has more inertia constant between turboalternator and hydroaltermanor and why?

2 Answers  


what is the difference between Resistance VS capacitance

2 Answers   Jindal,


I HAVE 2 nO'S OF SYSTEMS, HOW MUCH UPS CAPACITY REQUIRED ALONG WITH 400WATTS ANOTHER LOAD? PLEASE GIVE THE FORMULA?

1 Answers  


state the functions of different parts of star delta starter.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)