WHAT IS DGA TEST FOR THE TRANSFORMERS.
Answers were Sorted based on User's Feedback
Answer / jadhav padmakar
DGA Means Dissolved Gas Analysis. While in service
Transformer undergoes various termal,chemical,electrical
stresses due to that some gases generated these gases known
as Fault gases which r quantitified in extremely low level
in Parts Per Million (PPM), the test which is conducted to
analyse these fault gases known as DGA Test.
Is This Answer Correct ? | 65 Yes | 5 No |
Answer / pundlik wanwe
Transformer oil is a mineral oil. It is either parafinic
based or napthaline based. Oil contains the hydrocarbons.
When the oil get heted depending upon the temperature rise
oil gets decomposed and gassed begins to evolve.
To analise the composition of the evolved gasses the method
used is called Dissloved Gas Analysis.
Evolved gasses involves Hydrogen, Carbon monoxide, carbon
dixoide, methane, ethane, ethelyene, acetylene etc.
The samples oil is used to pass through the gas
chromatography where as per the temerature rise gasses
evolved can be seen as a spectrum band.
This method is a nice tool to judge the condition of oil in
transformer subsequentely that of transforrmer winding
insulation.
Is This Answer Correct ? | 51 Yes | 4 No |
Answer / anil kumar
DGA Means Dissolved Gas Analysis. While in service
Transformer undergoes various termal,chemical,electrical
stresses due to that some gases generated these gases known
as Fault gases which r quantitified in extremely low level
in Parts Per Million (PPM), the test which is conducted to
analyse these fault gases known as DGA Test.
Is This Answer Correct ? | 22 Yes | 3 No |
why we measure output of transformer in kva?
I'm looking for a mnaual set for a Teradyne J750. Softcopy would be preferred but I'll take what I can get.
WHAT is the no of starts/hr for 3.3 KV, 300 KW motor. Motor is vertical flange type.
A current of 2A flows for 10 hour through a 100 ohm resistor. The energy consumed by the resistor is:(a) 0.5 kWh(b) 4 kWh(c) 2 kWh(d) 0.02 kWh
how define the torque in ac drive. from electrical side in the drive friquency ,voltage and current three factor is there.
1.Can we use 6.6/11KV 300sq mm xlpe 3core cable for LT use (415 Volt). 2. If we use it for LT then what is the current rating
some meggers have three terminals. wat is the real function of the earth terminal?
if we look on phasor of the transformer vaoltage is 180 oppsite at primary and the secondary so to improve a power factor is secondary should kept negative to improve it primary side means is -.90 became +.90 at other side
What is single break or Double break related to MCB?
suppose generator rating is 50 kw,load is 25 kw,hw much d generator ll generate?what about d remainin power?
what is allowable current flows from phase to ground with out tripping the breaker
What is Minimum permicible meggering value for following 1) LT Panels (Ph to Ph / Ph to Earth) 2) 11 KV, HT Panels (Ph to Ph / Ph to Earth) 3) 11 KV Cable 4) LT Cable