what are the standards used for earthing instruments in the
field?
The internal screen is always floating at the instrument.
This means we just put some heat shrink on it to seal it and
then tie it off inside the instrument and just let it lie
there. The overall screen (braiding surrounding the cable
just below the pvc outside)will be in contact with the gland
once you have installed the gland. On the gland thread you
install a copper gland ring and a red IP washer, and the
gland then are attached to the instrument. From the gland
ring you use a six mm bolt and nut with copper washers to
attached a small diameter earth wire (about 4 to 6mm is
fine). This earth wire is then attached to the outside of
the instrument at the earth connection point on it's
housing. Every instrument will have this earth connector on
the outside of it's housing. From there you attached another
earth wire to the earth boss nearby. This boss is normally
just a piece of round bar about 40mm in diameter and about
30mm long and tapped in the middle that is welded to the
structure close by, specially for this earthing of the
instruments. Again it is better to use copper washers. If no
boss is available you can use some other point on the
structure as well like a stainless steel cable tray for
instance but the earth boss should really be part of the design.
On the other side of the instrument cable at the RTU the
internal screen in attached the instrumentation clean earth.
The dirty earth is used only for electrical equipment.
Good luck
| Is This Answer Correct ? | 3 Yes | 0 No |
what is lead lag compensator and for wat v using that???
in the construction field why hook up s.s.tubing for transmitter using upto 6mtrs of closed loop, but y not open loop nomore restriction
how to convert transmitter milliamps output to like temp,pressure etc.....
what step is taken for ESD ( emergency shut down) in DCS REPLY to hashimka20009@gmail.com
0 Answers Bosch, Eskom, Sabic,
hi all plz tell me difrence between analog or digital load cell.
What is meant by Fail Safe Condition in PLC?
What is the difference between DCS and SCADA?
Is it ok, to use non-contact type Radar type LT, on a tank that is half circular from the bottom side? If yes the, isn't the waves gonna bent in other directions?
0 Answers Process Control Technologies,
what is the difference about HART, and 4-20mA signal?
What is the calibration procedure of Drum level transmitter if range is 0 to -400 mmh2o in lab?
What is the working principle of the magnetic meter?
In control engg. : Differences b/w 1st order & 2nd order system, graphically & theoretically ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)