In an ammeter used for measurement of current, what is the
meaning of the representation of range as '0-50-300'?
Answers were Sorted based on User's Feedback
ABOVE REPRESENTATION SHOWS IT IS AN SUPPRESED SCALE OF
AMMETER
0-50-300A -------> IT MEANS IT MEASURES CURRENT FROM 0-50A
AND 300 INDICATES THAT 6 TIMES OF MAXIMUM CURRENT i.e
50*6=300
AT THE TIME OF SWITCHING CURRENT GREATER THAN THE NORMAL
VALUE
IT IS ABOUT 5-6 TIMES THE NORMAL VALUE
AT STARTING THE NEEDLE IN AMMETER GOES TO 300 AND WITH IN
FRACTION OF SECONDS COMES TO NORMAL VALUE
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / mahesh
It is a meter that can used in motor fdr. means motor FLC
is 50 Amp. & it's starting current is 6 times, i.e.300AMP.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / jay shah
It means the ammeter has a provision to select between 0-
50amps or 0-300amps full scale range.
Is This Answer Correct ? | 7 Yes | 6 No |
Answer / sella
THIS TYPE AMMETER WILL BE USED IN MOTOR FEEDERS. IF THE
MOTOR'S FULL LOAD CURRENT 50 MEANS IN STARTING TIME IT WILL
TAKE 50x6 TIME=300AMPS. THAT'S WHY WE ARE USING THIS TYPE
AMMETER IN MOTOR FEEDER. IN THIS AMMETER UPTO 0-50 AMPS
PROPERLY DEFINED IN DISPLAY BUT AFTER 50-300A THEY JUST
MENTION IN DISPLAY. IF WE USE NORAML AMMETER(0-50AMPS).IN
STARTING TIME METER WILL BE FULLY CLOSED FOR SOME SECOND
BECAUSE OF THIS METER ACCURACY WILL GO DOWN. IN NORMAL TIME
METER NEEDLE IN ACCELATION WE CAN'T MEASURE PROPER VALUE.
Is This Answer Correct ? | 0 Yes | 0 No |
For a Potential Transformer(PT), the primary neutral terminal must be grounded before energization. Why....? What will be heppend if we energize the PT without grounded the primary neutral point? Why..........?
Why do we use copper cable for HT Supply and why not Aluminium?
We use ACB in LT and VCB in HT.But if we use VCB in LT and ACB in HT that what will be the effect on the system or any power range?
The normal highest generated voltage in India is a) 6.6KV b) 132KV c) 11KV
Can anybody please refer the best and simple book for about Protection relays and in detail of all its protection ?
what is earthing.how we make it,describe briefly.
What are the different power system losses and how can it be eliminated?
why are the likely reasons for bochholz & pressure relays oprate due to a internal fault but not differential relay ?
what happens to the water pump if ground water level is slowly decreasing?our water pump is varying from no-load full-load due to this problem
What will be the effect of circulating current in HT xlpe cable when both the armour ends are grounded. Will the termination fils after some time in case of 33 kv supply.
how to calculate neutral current in three phase four wire system
In both 600/1000 V cable and 450/750 V cable, we can supply 415 V. However for distribution, all utilities are using only 600/100 V instead of 450/750 V. What is the reason?