the distance from my office to d.g is aprox 400mtrs and
voltage drops ibn my office near about 40 volt what should
i do p[ls suggest.
Answers were Sorted based on User's Feedback
Answer / sabale.dnyanehswar@gmail.com
IF U ASKING ABT DC Voltage then ans is
1. u have to increase the sq.mm size of the cable. i.e if
u r laid cable size is 16 sq.mm. u can go to 25 sq.mm.
2. u have to increase u r battery Amphour rating . by
replacing it with higher rating.
if u asking abt AC voltage:
1. check the DG set terminal voltage if voltage is not
proper then check at AVR terminal. if there also not ok.
then check it with another AVR card.
2. if AVR is OK then check any leakage of cable with taking
megger & continuty with earth.
3. if problem is found in cable then replace with new one
or increase the rating of cable.
if everythink is ok. then take voltage at receiver end with
out load. one by one increase the load at every time
voltage reading. if found prob. in another ckt. rectify it.
The range should be +- 5% should be accepted.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thowsif
Hi ,
Go through this link:-http://www.psihq.com/iread/faqvolt.htm
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / amit chaudhary
You should check the cable size which you are using from
your office to DG set. May it will need to increase the size
of cable.
If you are not using this DG set for another purpose then
you can increase the generator voltage by AVR to get the
suitable voltage in your office.
If the cable is heated during the load then you will have to
increase the cable size.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raj
Above all answers are right but one more we can do is to
add capacitor at load end to increase the voltage.
| Is This Answer Correct ? | 0 Yes | 0 No |
what will happen if i connect the buchholz relay in reverse direction.
Why we use a H.T. Fuse from a thick wire, on other side we use high rating of cables? & Why we use less Sq. mm Cable on H.T. side , on other side we use Large Sq. mm cable?
we r having 3 core 3 1/2, 4 core cables how we can know this cable has to be used for this purpose?
What is over fluxing in transformer?
What is VCB'S @ ACB'S.Plz explain Briefly
Meaning of CTPT ,how it works &how it measures the reading on trivecter meter,&what is trivecter meter
1 Answers PF, Student, TSSPDCL,
What are the different pre-commissioning tests that are performed on the distribution transformer, power cable and switchgear (11kv)?
1. A 380 / 220 V r.m.s. 3-phase 4-wire circuit carries loads of 8 + j8.1 ohm; 4 + j4.1 ohm; and 2 +j2.1 ohmin the three phases respectively. The length of the circuit is 100 m, and the resistivity of the phase conductors is 0.0005 Ω/m. The neutral conductor is of the same size as the phase conductors. a) Select a reference angle 0for the first phase. Then write down the three phase voltages in both polar format and complex number format. b) Make appropriate assumptions, and take temperature effects on resistance is insignificant. Calculate the currents in the three phases. (Note: Determine conductor resistance, and apply Kirchhoff’s Voltage Law) Based on the result, suggest a main switch rating for the circuit. c) Show your preferred direction of neutral current in a diagram, and then determine its value. (Note: Apply superposition principle, and Kirchhoff’s Current Law) Use its magnitude to show that in this circuit, the unbalanced load may increase the voltage drop in some of the phases. (Note: Also observe the common volt drip in neutral) State your assumptions, if there are any. d) Suddenly the neutral wire of the circuit is broken. Estimate the new currents in the first phase, i.e. Phase L1. State your assumptions, if there are any.
What is control system?
why are you use the crgo core lamination in transformer
what is the significance of terminal voltage and phase sequence in the operation of paralleling of two generators?
formula for incomer breaker size calculation of powerfactor correction unit
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)