the distance from my office to d.g is aprox 400mtrs and
voltage drops ibn my office near about 40 volt what should
i do p[ls suggest.
Answers were Sorted based on User's Feedback
Answer / sabale.dnyanehswar@gmail.com
IF U ASKING ABT DC Voltage then ans is
1. u have to increase the sq.mm size of the cable. i.e if
u r laid cable size is 16 sq.mm. u can go to 25 sq.mm.
2. u have to increase u r battery Amphour rating . by
replacing it with higher rating.
if u asking abt AC voltage:
1. check the DG set terminal voltage if voltage is not
proper then check at AVR terminal. if there also not ok.
then check it with another AVR card.
2. if AVR is OK then check any leakage of cable with taking
megger & continuty with earth.
3. if problem is found in cable then replace with new one
or increase the rating of cable.
if everythink is ok. then take voltage at receiver end with
out load. one by one increase the load at every time
voltage reading. if found prob. in another ckt. rectify it.
The range should be +- 5% should be accepted.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / thowsif
Hi ,
Go through this link:-http://www.psihq.com/iread/faqvolt.htm
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / amit chaudhary
You should check the cable size which you are using from
your office to DG set. May it will need to increase the size
of cable.
If you are not using this DG set for another purpose then
you can increase the generator voltage by AVR to get the
suitable voltage in your office.
If the cable is heated during the load then you will have to
increase the cable size.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raj
Above all answers are right but one more we can do is to
add capacitor at load end to increase the voltage.
| Is This Answer Correct ? | 0 Yes | 0 No |
why induction motor takes high current?
3 measuring instrument for transformers?
IN 3 phase induction motor where we give i/p supply & how its working ?
What happen in ups if phase reverse?
What is the use of mc( moving coil) in dc voltmeter and dc ammter and what is the use of ( moving iron)in ac voltmeter nd ac ammeter
a distribution transformer(3 phase)supplying 440volt per phase.now suppose one of phase voltage(230volt) becomes zero.what will be the cause ?
why Current is lead 90 degree and voltage is lag 90 degree in a capacitor.? why Current is lag 90 degree and voltage is lead 90 degree in an inductor.?
what is the method of earthing of a transformer using electrodes?
what happen if drive input fail momentry at 48.5 HZ frequency?
how to calculate regulation constants for over head lines? and what are the regulation constant for raccoon conductor at different voltage level and different P.F?
how the harmonics are generated in transforemer?
WHAT IS SPEC OF CLEANROOM MOTOR AND LIGHT FITTINGS?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)