no EB power DG is not starting?
Answers were Sorted based on User's Feedback
Answer / prashant
Check if the DG is starting . If not check ur AMF panel and
the corresponding relay
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / selvan
which mode DG set connected?
manual mode- 1.battery terminal or its cable demaged.
2. low volt in battery.3. self motor problem.
4.fuel block.
auto mode- 1.EB power failure comand not going to dg
control panel. 2. DG CONTROL panel not reset.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / nagaraj.m
this is fully interlock system so this is not working in eb
power dg is not starting
| Is This Answer Correct ? | 5 Yes | 2 No |
if the DG is in auto mode
1)Signal may be not reaching the DG from main panel.
2)Battery may not have enough charge to crank the DG.
3)Shortage of fule in DG or flow of fule to th DG may have
problem.
4)In case of more no of DG controle wiring may have problem.
5)synchronization off DG may have problem.
6)phase sequence may have problem.
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / sreekanth
plz check the battery of dg.if it is totally discharged
then dg will not start
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / elangkumanan
dg set battery discharging problem.
auto mode sanner not working.
fuel was low.
radiator water level was low.
| Is This Answer Correct ? | 0 Yes | 1 No |
What is the impedence of Transformer?
Sate maximum power transfer theorem?
IN 1000kva transformer where the oil and winding temperature sensors is connected
If one ct is reversely connected in Y system what will effect in kwh and kvarh meter?
details of oil cell size of Breakdown voltage test of tranformer oil details as per Standardswith mushroom electrodes?
In distribution transformers, fuse wires are very thin when compared to conductor size. How it's possible?
Explain Circuit Breaker Trip Characteristics in detail.
IR value for 30kw lt motor
What is the difference between the impedance percent and impedance voltage ?
What is the function of RCCB? What are the different sensitivity ratings & each application?
i wanna know that star point in transformer becomes as a neutral on secondary side now tell me that how is that possible?because if joit the all three winding ends with each other it can b short circuited.dut it doesn't.WHY?pls Answer me in brief.thanks alot
why there is a 2 slits in three pin's earthing pin?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)