no EB power DG is not starting?
Answers were Sorted based on User's Feedback
Answer / prashant
Check if the DG is starting . If not check ur AMF panel and
the corresponding relay
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / selvan
which mode DG set connected?
manual mode- 1.battery terminal or its cable demaged.
2. low volt in battery.3. self motor problem.
4.fuel block.
auto mode- 1.EB power failure comand not going to dg
control panel. 2. DG CONTROL panel not reset.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / nagaraj.m
this is fully interlock system so this is not working in eb
power dg is not starting
Is This Answer Correct ? | 5 Yes | 2 No |
if the DG is in auto mode
1)Signal may be not reaching the DG from main panel.
2)Battery may not have enough charge to crank the DG.
3)Shortage of fule in DG or flow of fule to th DG may have
problem.
4)In case of more no of DG controle wiring may have problem.
5)synchronization off DG may have problem.
6)phase sequence may have problem.
Is This Answer Correct ? | 6 Yes | 5 No |
Answer / sreekanth
plz check the battery of dg.if it is totally discharged
then dg will not start
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / elangkumanan
dg set battery discharging problem.
auto mode sanner not working.
fuel was low.
radiator water level was low.
Is This Answer Correct ? | 0 Yes | 1 No |
How can ignition voltage of light increased with the help of a ballast
A 3-phase IM is supplied from 50 Hz system. It runs at speed of 1440 rpm and slip equal to 4 %. Calculate rotor frequency. A 50 Hz B 0 Hz C 4 Hz D 6 Hz
hi I have done 3 yrs diploma in electrical engg after 10+2. I have 16 years of work experience into design proposals sales and engg application development in LV/MV swithcgear and sub station automation field. I want to apply for immigration to new zealand but I am not sure whether I qualify or not since I dont have a degree. Can anyone advice? Thanks Riz
WHAT IS AIR GAP VALUE IN MM FOR A 11KV BUSHING OF 11KV/440V DISTRIBUTION TRANSFORMER. AND AIR GAP VALUE OF 25 KV BUSHING OF AT TRANSFORMER OF 25 KV TRACTION. WHAT IS THE CALCULATION FOR THE AIR GAP PERMITTED FOR BUSHINGS AT DIFFERENT VOLTAGES.
how current is reverse from its normal direction during the fault?
IN dc capacitive reactance is??
what are smoke detectors ?
4 Answers Indian Military Services,
what is meant by auto transformer?
1.dg on load alarm/stop alarm... 2.dg on load. piu alarm alarm kaise chek krte hai
how to calculate the power factor when instantaneous voltage and current has harmonics in it ?
We have a 33/11kv switchyard having 12.5 MVA power transformer. We export & import power through this transformer. When we export power, the PF will be depend on GRID PF & when we import power the PF will be depend on our load PF. but the problem is that,when neither we export nor import but our 33KV vCB is in close position,our meter read the power factor 0.14 to 0.25 at that moment. So how can be we improve the power factor at that moment.
what is buffer resistance starter.?.What is the working principle and where it is used..?