How we check vector group for a Dyn1 transformer?
Answers were Sorted based on User's Feedback
Answer / s.ravindra
The condition of dyn1 was
(a) 1W2N+1U2N=1U1W
(b) 1W2W=1W2V
(c) 1V2W >1V2V
| Is This Answer Correct ? | 14 Yes | 1 No |
Answer / gunasekaran
we can find out from ratio kit
if applied UV-vn get energised
if applied VW-wn get energised
if applied WU-un get energised
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / vinod maurya
We will short 1U & 2U
And we will apply 3 phase voltage between 1U,1V,1W
Measure between
1U-1V
1V-1W
1W-1U
1V-2v
1V-2w
1W-2w
1W-2v
1W-2n
2n-1U
Verify The Condition
1W-2n+2n-1U= 1U-1W
1W-2w=1W-2v
1V-2v<1V-2w
vector group Dyn1 confirmed if the above conditions are
satisfied.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / y.rama krishna
Connect 1U&2U
Apply 3ph 415V balanced voltage across terminals 1U,1V,1W
(HV wdg)
Measure the voltages between the given terminals & record
1)1U-1V
2)1V-1W
3)1W-1V
4)1V-2V
5)1V-2W
6)1W-2V
7)1W-2W
8)1U-2N
9)1V-2N
Verify the conditions
a)1W-2W = 1W-2V
b)1V-2W = 1V-2V
c)1U-1V = (1U-2N)+(1V-2N)
vector group Dyn1 confirmed if the above conditions are
satisfied.
| Is This Answer Correct ? | 18 Yes | 16 No |
Answer / mahmoud moustafa
The condition of dyn1 was
(a) 1W2N+1U2N=1U1W
(b) 1W2W=1W2V
(c) 1V2W >1V2V
this is correct I check today in one of GE sites
| Is This Answer Correct ? | 2 Yes | 0 No |
the parts of transformers ?
1 Answers Bhel, Facility management,
what is the working principle of three point starter of dc motor?
1 Answers Ashok Leyland, Cap Gemini, Infosys, Just Dial,
All the voltage drops and the source voltage added together in a series circuit is equal to
what are the protecyion of transformer & generators
If we have 15000kw connected load in a factory than how much power demand sanction should be taken from electricity board. Pls provide complete calculation.
When MICC cables used ?
why we used servo motor insted of inducation motor?
How do you select the pickup value of the relay?
what is LOS(line of sight)?
sir iam from electrical and electronics branch ,can i appear for the hpcl offline requirtment? if yes please mail me on vikram_raju25@yahoo.co.in
I have 725KVA DG set how to Calculate the Ratio of KWH? Whatb is the Formila
What is the meaning of coupling and decoupling in the context of power flow?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)