How we check vector group for a Dyn1 transformer?
Answers were Sorted based on User's Feedback
Answer / s.ravindra
The condition of dyn1 was
(a) 1W2N+1U2N=1U1W
(b) 1W2W=1W2V
(c) 1V2W >1V2V
| Is This Answer Correct ? | 14 Yes | 1 No |
Answer / gunasekaran
we can find out from ratio kit
if applied UV-vn get energised
if applied VW-wn get energised
if applied WU-un get energised
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / vinod maurya
We will short 1U & 2U
And we will apply 3 phase voltage between 1U,1V,1W
Measure between
1U-1V
1V-1W
1W-1U
1V-2v
1V-2w
1W-2w
1W-2v
1W-2n
2n-1U
Verify The Condition
1W-2n+2n-1U= 1U-1W
1W-2w=1W-2v
1V-2v<1V-2w
vector group Dyn1 confirmed if the above conditions are
satisfied.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / y.rama krishna
Connect 1U&2U
Apply 3ph 415V balanced voltage across terminals 1U,1V,1W
(HV wdg)
Measure the voltages between the given terminals & record
1)1U-1V
2)1V-1W
3)1W-1V
4)1V-2V
5)1V-2W
6)1W-2V
7)1W-2W
8)1U-2N
9)1V-2N
Verify the conditions
a)1W-2W = 1W-2V
b)1V-2W = 1V-2V
c)1U-1V = (1U-2N)+(1V-2N)
vector group Dyn1 confirmed if the above conditions are
satisfied.
| Is This Answer Correct ? | 18 Yes | 16 No |
Answer / mahmoud moustafa
The condition of dyn1 was
(a) 1W2N+1U2N=1U1W
(b) 1W2W=1W2V
(c) 1V2W >1V2V
this is correct I check today in one of GE sites
| Is This Answer Correct ? | 2 Yes | 0 No |
In a company the lines carrying 33KV but the load is below 10000Volts so we know that <11KV we can put 11KV lines but the lines are 33KV,..so how we can step down the voltage to 11KV with out erecting a substation
How short circuit MVA(Fault MVA) in a power system calculated for calculating number of earth plates ?
Why we use 2core cable for Dc motor.Can I use 3core?
5 Answers JK Paper, Maharaja Whiteline,
why do we prefer -48 volt instead of -24volt or -12 volt etc. ??
The neutral&earth voltage is 0v.But we were connected the lighting load at the time ballast was failed.why?
can we synchronize star system generators with delta system generators?
What are safety seals?
Difference between SHORT CIRCUIT and an OVERLOAD ?
Control cables in S's will carry 1000v which is AC R DC? Pls answer me
Why voltge arev transformed in to 132KV/66/KV/33KV like that
What happens when generator is running with leading power factor on it say -0.96. what are the effects of it on alternator and the other generators operating in parallel to it.
HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT-SWITCH BOARD,MLDB,ACB,BUSBAR,ETC,......?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)