How we check vector group for a Dyn1 transformer?
Answers were Sorted based on User's Feedback
Answer / s.ravindra
The condition of dyn1 was
(a) 1W2N+1U2N=1U1W
(b) 1W2W=1W2V
(c) 1V2W >1V2V
| Is This Answer Correct ? | 14 Yes | 1 No |
Answer / gunasekaran
we can find out from ratio kit
if applied UV-vn get energised
if applied VW-wn get energised
if applied WU-un get energised
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / vinod maurya
We will short 1U & 2U
And we will apply 3 phase voltage between 1U,1V,1W
Measure between
1U-1V
1V-1W
1W-1U
1V-2v
1V-2w
1W-2w
1W-2v
1W-2n
2n-1U
Verify The Condition
1W-2n+2n-1U= 1U-1W
1W-2w=1W-2v
1V-2v<1V-2w
vector group Dyn1 confirmed if the above conditions are
satisfied.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / y.rama krishna
Connect 1U&2U
Apply 3ph 415V balanced voltage across terminals 1U,1V,1W
(HV wdg)
Measure the voltages between the given terminals & record
1)1U-1V
2)1V-1W
3)1W-1V
4)1V-2V
5)1V-2W
6)1W-2V
7)1W-2W
8)1U-2N
9)1V-2N
Verify the conditions
a)1W-2W = 1W-2V
b)1V-2W = 1V-2V
c)1U-1V = (1U-2N)+(1V-2N)
vector group Dyn1 confirmed if the above conditions are
satisfied.
| Is This Answer Correct ? | 18 Yes | 16 No |
Answer / mahmoud moustafa
The condition of dyn1 was
(a) 1W2N+1U2N=1U1W
(b) 1W2W=1W2V
(c) 1V2W >1V2V
this is correct I check today in one of GE sites
| Is This Answer Correct ? | 2 Yes | 0 No |
what is meant by oil filled power & distrubution transformer ? if anybody know the link of detail about above transformers means plz send it i have interview on this week ? plz help me
Can we use 230VAC, 63A MCB for 120VAC, 63A supplied heaters load?
Why Nutral CT rating for Earth Fault Protection of Transformer neutral shall be 20% of Full load Current of Transformer
what is the difference between current rating and breaking current of an MCCB? and for a known load how to calculate the current rating of a MCCB?
what are the major difference between 3phase 3wire and 3phase 4wire trivector meter?
how to calculate load if i have three phase & single phase connection from power transformer( in term of kw & kva).can i take single phase load/3 for total kw calculation
explain the meaning of harmonic resonance
Shunt reactor is used in EHV Transmission line for..............?
Enlist four components of electrive drives.
100 MVA 3-phase alternator with earthed neutral has a reactance of 5 ohms per phase. what will be the fault MVA of generator.
On a 3 winding transformer YNynd11, how do you apply REF protection to the Delta tertiary winding that is supplying auxiliaries to a substation?
what u meant by shock ? whether it depends on voltage or current
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)