I am working on a 11KV system with fault current of 40KA
for 1 second. I have selected 2500MVA 11/0.433KV
transformer.
How can i find the impedance value for this transformer?
Please help me.
Answers were Sorted based on User's Feedback
First I do not believe an 11 kv system can have a 40ka
fault. You need to check again.
Second I do not believe you can connect a 2500 mva
transformer to an 11 kv system. Maybe 2500 kva.
%Impedance is on the nameplate of the transformer or ask
the manufacturer.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kaushik
i don't understand the purpose of giving 1 second ......
but what i think solution will be
s.c mva=1.732*v*i.
s.c mva=1.732*11000*40000.
s.c mva=762.08 mva.
per unit impedence of the transformer will be= (base
mva)/(s.c mva)
taking transformer 2500kva(i think it is wrong 2500mva)
we get
=(2.5/762)*100=0.328% of tranformer impedence
Is This Answer Correct ? | 0 Yes | 0 No |
what is EIB lighting control system? what is the advantages of this system?
how to select the automotive wire size by mathematical calculation. for xenon headlamp with ballast. the ballast given data voltage 10-17v,current permenant 6amp, run up phase is 15amp, peak at swicth on max 400micro sec is 40amp.the sum of cable resistance is 150mohm.please provide referenc document if any for relating the peak at switch on current,time & wire wire size
What is transister define the transister ammiter ,base, colector.
What may be happen if neutral and earth is shorted in a substation
What is the function of lead sheath?
what is mean by current
If there is major % of Voltage harmonics in the system, how can it be control or reduced?
how to maintain standard votage in power system?
I WANT HOW CALCULATE TO CABLE FOR WELDING PLANT ?
What is the relationship between the sending end and receiving end?
There is air in a room . the top and bottom of the room are at constant temp. T1 and T2. DRAW THE temp profiles if a. T1 greater than T2 b. T1 less than T2
What is difference between potiential,volatge and emf