what happens when a power transformer neutral earthing
broken???
Answers were Sorted based on User's Feedback
Answer / privin p v
according to KCL midpoint of a star connection is zero potential.If the load of the transformer is balanced nothing happen while neutral earthing broken.But in case of any unbalancing occurs there is no way to go the circulating current and heat occurs.It will damage the transformer
| Is This Answer Correct ? | 14 Yes | 1 No |
Answer / tejpratap pandey
trnsformer phae to neutral voltage unbalanced & its may
dammage load side equipment.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / r.ramadoss
Netural is providing in the transformer for passing 3rd
assymentrical current , if the netural was not present ,
due to the surge voltage or un balanced voltage the
transformer life time will be decreased
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / anand
harmonics will increase and sinusoidal output will tend to
become a bit nonsinusoidal
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / dk gnfc
When neutral open,line voltage flowing in phase,so overvolage occurs in all phases,and if REF provided,it will trip the transformer as protection against neutral opened from earth
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nagaraju n
in this condition is un safe condition .
transfarmer is become fail to operation.& become a dameged
| Is This Answer Correct ? | 2 Yes | 7 No |
Answer / srinivas
there is a standby earthfault will occur on load side.
| Is This Answer Correct ? | 0 Yes | 6 No |
Answer / thuranga
Normally any power or normal transformers is designed in
such a way that all the three phases will be 99.9% balanced(
winding wise).
so neutral in transformer is not at all needed,but for extra
protection neutral is put.
so if the neutral is not present,there may not be any much
change in its operation but vibration of the transformer
might increase.only that will be the change.
| Is This Answer Correct ? | 4 Yes | 13 No |
How CFL &T5 tube light glows?
please explain me about traction application?
what shall be no load voltage of 132/33 kV transformer ? is it 33 kv of 34.5 kV
Why are the laminations insulated from each other?
How to Decide(calculate) Bush bar size for copper and aluminiam ?
The moisture in air will condense at
why C.T protection required for H.T.lines?
what is the condition for YnD11
hi Is there any possibilities to find out the rotation of a shaft or something else by using electromagnectic waves or by IR rays.If s then can v change the dir., of rotation of the same by remotely?& how? plz dn't any1 say "NO r CAN'T"
How much allowable difference current between on three phases Dear sir, We have a 1870 KW HT motor, 11 Kv supply,FLA-120A,2870 rpm,2-pole squirrel cage induction Motor.And stator is connected in star connection with Liquid resistance stater to limit the starting current.It has coupled with Centrifugal air compressor.My question is it is loading 73% of FLA taking R-phase 86.7 A, Y-phase-85.4A,B-phase- 78.3A.why the B phase current is that much of difference.Is it allowable, or any one tell me how much allowable current.If any method to calculate.
which INDIAN STANDERD in Mention the earth test value?
what is metering cum synchronizing panel and how it is used?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)