what happens when a power transformer neutral earthing
broken???
Answers were Sorted based on User's Feedback
Answer / privin p v
according to KCL midpoint of a star connection is zero potential.If the load of the transformer is balanced nothing happen while neutral earthing broken.But in case of any unbalancing occurs there is no way to go the circulating current and heat occurs.It will damage the transformer
| Is This Answer Correct ? | 14 Yes | 1 No |
Answer / tejpratap pandey
trnsformer phae to neutral voltage unbalanced & its may
dammage load side equipment.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / r.ramadoss
Netural is providing in the transformer for passing 3rd
assymentrical current , if the netural was not present ,
due to the surge voltage or un balanced voltage the
transformer life time will be decreased
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / anand
harmonics will increase and sinusoidal output will tend to
become a bit nonsinusoidal
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / dk gnfc
When neutral open,line voltage flowing in phase,so overvolage occurs in all phases,and if REF provided,it will trip the transformer as protection against neutral opened from earth
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nagaraju n
in this condition is un safe condition .
transfarmer is become fail to operation.& become a dameged
| Is This Answer Correct ? | 2 Yes | 7 No |
Answer / srinivas
there is a standby earthfault will occur on load side.
| Is This Answer Correct ? | 0 Yes | 6 No |
Answer / thuranga
Normally any power or normal transformers is designed in
such a way that all the three phases will be 99.9% balanced(
winding wise).
so neutral in transformer is not at all needed,but for extra
protection neutral is put.
so if the neutral is not present,there may not be any much
change in its operation but vibration of the transformer
might increase.only that will be the change.
| Is This Answer Correct ? | 4 Yes | 13 No |
I have applied the post Junior Engineer-iii(c&w)in R.R.B chennaI recently . can i get any model question paper LAST 4 YEARS?
2 Answers Data Entry Operator, RRB, SSC,
how is motorized megger operate?
what are the safety measure & controls in engine?
if there is nutral in phase why we use earthing wire and grounding? even at fault condition the fault current flows to neutral (it is a lower path)
what is the name for a meter/tester to measure the paint quality in electrical panel or wall?
What is magneto on a gas generator. how it functions. its out put is d.c or a.c. how it can be checked for correct functioning
As we know induction squirrel cage motor torque Directly praprortinal to applied voltage in star connection & delta also. If I connect 55KW Motor to DOL starter in load condition does motor withstand the load & what will be the current withdrawn ? motor will not fail ?
how we calculate the 30 KW 3phase electric motor current on noload
23 Answers Monnet, Siemens, SSR, Supermac Industries,
Why 50hz and 60hz frequencies are used by the world, why they are not taking 55hz?
auto reclosing scheme for radial ehv feeder is to be implemented or not?
what are the dimensions for 200 kva transformer plinth (plateform),in which pcc m20 is used..
Installation resistance for whole installation of 16 kva & 25 KVA DTRA a) Between each conductor b) between conductor to earth c) installation resistance for each apparatus, each conductor to earth d) earth resistance for the system of earthing
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)