THE 40 MW OF POWER FOR 220 V III PHASE POWER CONNECTION
REQUIRES HOW MANY KVA POWEER REQUIREMENTS
Answers were Sorted based on User's Feedback
Answer / reshi
If we assume the power factor during motor running as 0.85.
Then the calculation will be 40MW/0.85= 47MVA.Answer.
| Is This Answer Correct ? | 10 Yes | 4 No |
Answer / riyadh
this formula u going to apply
Kw=Kva*P.f
we know P.f = 0.9 for T/f's
P.f = 0.8 for Generator
we knw power kw 40Mw
Apply to above formula Kva = kw / p.f
Kva = 40000 Kw / 0.8
Kva = 50000 kva
In Mva is 50
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / chethan
p- 40MW,v,220volts kva=?
40*1000000*4.54Amps multiply (1000=1.732*220*I,ans.4.54)
Ans. 181600 KVA
this is my knoldge ,so this is error,please tell me the
correct answer.
| Is This Answer Correct ? | 0 Yes | 0 No |
Its 50000Kva on .8 pf and answer#3 is correct.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jayaraj
The question is wrong. 40MW load could not be fed from 220v 3 ph system. If the question is the KVA requirement 50000KVA on .8 pf. So in a distribution system 2000KVA Transformer 25 nos are required.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / v.s.narayanaswami
THE ABOVE FORMLA APPLIES FOR CONVERSION OF HP INTO KVA AND
THE CORRECT CONVERSION FACTOR IS 0.764.
THE REQUIREMENTS OF 40 HP CONNECTION CONVERTED INTO KVA
APPLYING THE FORMULA IE 1 HP = 0.764 KVA IS 40HP/0.764 IS
APPROXIMATELY IS 52 KVA.
HENCE UR CORRECT REPLY IS SOLICITED FOR ARRIVING AT THE KVA
DEMAND FOR THE ESTIMATED 40 MW OF POWER CONNECTION
REGARDS
V.S.NARAYANASWAMI
B.COM(HONS), M.COM, F.C.A
| Is This Answer Correct ? | 2 Yes | 12 No |
What are the disadvantges of leading power factor
why a motor overheated stops to rotate ?????
when a cunductor is being disconnected from live cct, still it showing charged, if its checked by line tester?
How can we calculate the motor frame sizes?
What is OLTC in a transformer, specify its fuction.
35 Answers Bhel, Isgec, L&T,
How reverse power relay sense the power is reverse in the system.
what is vector surge & vector shift? we have 25.3 MW(11kv) generator & 11kv/132kv transformer, connected with with 132 kv grid.vector surge relay is tripping frequentaly.what is permissible maximum limit for this.
which gas is cost wise high?
What do you mean by phasors?
can anyone give an idea about dia calculation in cold rolling mill
which pump is suitable for home use ?
WHAT IS THE WINDING PROCEDURE OF ELECTRICAL MOTOR
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)