How the Transformer oil testing is done & Why oil dielectric
goes LOW & what is solution for that ??
Answers were Sorted based on User's Feedback
The sample oil to be tested for dielectric test is collected
and put into the tester and the average of 6 tests is
taken.The minimum withold voltage is as per local regulations.
causes of low dielectric results are usually exposure of the
insulating oil to moisture through the breather or there is an
exposed opening, poor quality oil being used. high acidic
content.The insulating oil should be replaced or dehydrated.
breathers silica gels should be maintained good all the time
and check for any leaks or any exposure to atmosphere must be
rectified.
| Is This Answer Correct ? | 15 Yes | 1 No |
Answer / ravikumar.g
The transformer Oil testing to be done in filtration unit
by checking the Oil Testing Kit in KV
20 KV low
when the voltage are not balancing properly and the taps
are changing regurly the oil becomes carbonsied this
carbonsied oil is acts as conductor.
So these problem so we change the Oil.
The salution for this changing the oil the transformer has
to be oilfilteration in once in a year.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / saroj
TRF oil is tested in a glass pot where high voltage,KV is
applied between two electrodes and sparking at electrode to
be observed. For good oil , it comes about 40~60KV/mm .If
it comes lower then filteration is required. Those TRF
having tap changing is frequently required it is
recommended to do filteration in once in year.Also its
value goes low because of moisture ingress in oil .
| Is This Answer Correct ? | 5 Yes | 1 No |
What is NUMBER OF RUN for power cable means?
how an electron flow in a wire. can it flow like a car running on the road?
Is it really necessary to have reactive power in transmission line to transfer the power from one place to other?
Buchholz relay is used ………. a) protection T/F b) oil T/F c) Air core T/F
8 Answers Engineers India Limited,
rrb question
why the difference arise between HT reading & LT reading (submeters fixed in complexes, apartments etc)if the power factos exceed from 0.9 to 1 can the ht meter reads fast?
what is the principle of synchronous motors?
how to find out three phase motr kw with out name plate..
how we can explain arc heatng?
What is the resonant peak?
why we not use capcitor in Three phase motor ??
2 Answers GOMS, Power Electronics,
i need to calulate the cable size when watts are mentaind wat z the formula
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)