What is VCB? Where it is installed?
Answers were Sorted based on User's Feedback
Answer / n.p
vcb full form is vaccum circuit breaker. its contacts arc
quenching medium is vaccum. vcb used in 11kv ht line for
on/off operation.
| Is This Answer Correct ? | 83 Yes | 6 No |
Answer / amit upadhyay dscl
VCB is a vaccum circuit breaker inwhich uses vaccum for
medium. it is installed in HT side of line i.e. 11kv.
| Is This Answer Correct ? | 46 Yes | 2 No |
VCB means vaccum ckt breaker it can be used at any voltage
but due to its high cost it is generally used at HT side.
contacts of vcb operates in vaccum chamber.
It have spring charge moter,spring is used to operate
moving contacts.
It have closing & tripping coils & auxillery contact switch.
Can be operated manually also
| Is This Answer Correct ? | 22 Yes | 6 No |
Answer / swamy
VCB stands for vacume circuit breaker. it is get contact by
produceing arc in vacume.VCB is used in HT side ie 11kv and
above.
| Is This Answer Correct ? | 21 Yes | 8 No |
Answer / pankaj
VCB means VACUUM CIRCUIT BREAKER.In this vacuum are used as a arc quenching medium.
It can be use for 3.3kv to 36kv. Generally it is used in indoor sub-station.Also OVCB is used in Outdoor sub-station.
| Is This Answer Correct ? | 14 Yes | 7 No |
Answer / saroj senapati
vcb means vaccum circuit breaker. when any fault has arise the circuit then it is tripped ,example the short circuit,earth fauth over current has arised...
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / hasan mehdi
VCB is Vacuum Circuit Breaker. It is installed in 11 kv RMU
(Ring Main Unit) System.
| Is This Answer Correct ? | 10 Yes | 7 No |
Answer / rod
Answers 1 and 2 are partly correct, however they can be
used on any voltage from 440volt to around 40.5 kV, I
currently use them on sump pump motors 60kW 440 volt but
have used themon 33kV
| Is This Answer Correct ? | 10 Yes | 8 No |
Answer / ravi kumar
VCB Means vacuum circuit breaker, its contact arc quenching medium is vaccum ckt breaker its used in ht line .
safety: earth fault relay , master trip relay, supervision relay,
its used for main supply ON and OFF with safety .
Its using supply test faulty condition and unfaulty condition.
| Is This Answer Correct ? | 0 Yes | 0 No |
VCB stands for Vacuum Circuit Breaker
As the name suggests that the phenomenon of arc quenching will happen in Vacuum medium.
It is generally used in MV applications(3.3-36KV)
The main advantages of VCB being it has high dielectric strength(8 Times higher than air and 4 times higher than SF6) which makes it easier to quench the arc with less gap between the contacts. Also the life of VCB is considerably high owing to less maintenance and ease of Vacuum bottle replacement. Also unlike SF6 it is not a harmful to environment and less dangerous comparative to OIL CB. Generally the pressure maintained in Vacuum chamber is 10^-6 bar.
Regards
Raviteja V
| Is This Answer Correct ? | 2 Yes | 3 No |
Difference between SHORT CIRCUIT and an OVERLOAD ?
what is the condition for YnD11
Why LVDT have secondary windings connected in differential 1. Higher out put 2. Based on the out put voltage-/+, helps to identify the direction of displacement 3. To establish a null/ reference point
What will happen if 33 kv is given to a 11/0.415 kv Distribution transformer?
EXPLAIN THE TERMS "INTEREST AND DEPRECIATION" AS APPLIED TO ECONOMICS OF POWER GENERATION.
why impudance relay used for medium transmission power system? why not others?
why do transformer humm ??????????
how to select the rating of neutral ct with reference to transformer secondary current(in power transformer,stepdown tansformer,for example2000kva,11kv/415volt
to transmit 30kw of power at 30 km what is voltage required
2 Answers Anglo Eastern, Merchant Navy, NPCIL,
We are having a 2000KVA DG set. It trips with Over speed and Engne Hot when the mahine is stopped in full speed. How shall I analyse the block load and reverse power.Is the problem related to power factor. The machine which runs on this DG is having all Synchronous motors with incividual Drives.
For a certain load i need 100kw load ,In that case what rating mccb should i use?
How can we prevent the (Home)inverter supply flow to the main supply line?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)