How to test Power Transfomer vector group in the field?
Answer Posted / chicoybolanio
Put the tap position on the nominal taps.
Connect the 4 core cable with MCB on the HV side and the
leads cable at LV side and make sure that
the LV side in open circuit. Then loop together between HV
red phase and LV red phase.
Inject 415V (Switch on the MCB) at HV side and measure the
voltage at LV side for each phase. record results and by
using the test result and following proper scale draw the
vector group of the transformer winding.
| Is This Answer Correct ? | 11 Yes | 1 No |
Post New Answer View All Answers
Define resonant frequency?
If any HVDC line is going with positive & negative(the negative usually have return path of current with earthing electrode). Now the question is if this HVDC earthed electrode which is using as return path and earthed any nearby 400kv or 220kv AC substation equipments. which will be the impact of this on AC substation & its equipment, how severe may be this and what should be the minimum distance require between HVDC earthed electrode and AC substation equipments? It's really an high engineering level question...Dare to answer and increase your knowledge.
I have a situation to design sub-Distribution board/Panel meant for feeding power sockets. In the incomer CAN i Take TP MCCB with Neutral Link and All the outgoing feeders with to sockets with TP MCCB and Neutral Link? P.S : My System is IT Earthing
How to calculate the fuel consumption for 600kva DG genset which connecting with 25%load?
what is mean by restructuring power system?
it is possible to measurement of tension of slipring induction motor(SRIM)carbon brushes, any maesuring instruments are available in the markets.
what is the difference between the characteristics of two different phase bushing of any transformer
how to decide no of electrodes for 1600A LT Main incomer panel
How does a tertiary winding filter harmonic(espcially 3rd one) from entering into load system?
How a band pass filter is constructed?
hi....I am from india..i have completed my engineering in electrical and electronics field with 58.4% and my IELTS score is 5.5 bands....Recently i received my I-20 in computer and information science from Troy university in Alabama.On 18th i have a visa interview can u please tell me what type of questions i have to answer ??????
what is the total power generation in india?
Can anyone please give me the parameters , formula needed to calculate the circuit breakers for building services.Thanks
where we use the SFU & FSU?
I am inpecting a 10kVA UPS what tests should i do and should i observe?