what is the difference between inrush curent and jurk load.
Answers were Sorted based on User's Feedback
Answer / anthony
The inrush current is that value of current used to
overcome the inertia presented by the magnetic dipoles to
the impinging flux . The dipole resists the change in the
turning moment produced by the mag. field ( when machine is
started from rest state).
The jerk current is that value of current that is
drawn in excess of the already supplied current while the
machine is still in operation.
The jerk current is not required to oppose the moment
offered by the magnetic dipole , whereas the inrush current
is used to induce magnetism in a metal and hence overcomes
the dipole moment .
This is the striking diff. between the inrush current
and the jerk current
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / s s nanal
In case of AC Motor Inrush current is current drawn by
motor while at start.This inrush current is very high (
almost 5 -6 times full load current.) The reason is,at
start the back emf offerred is zero.This back emf is
developed as the rotor gains speed.Hence at start Current
drawn by motor is equal to Voltage divided by impedance of
stator winding( winding impedance is very low,hence
starting current is high.) Once the rotor gains speed
current drawn by motor is equal to Voltage- Back emf/
impedance.As back emf is developed now the motor draws less
current.
Jurk Load is current drawn by motor already running.But due
to jurk load motor draws high current in order to maintain
speed ( near synchronous speed)
| Is This Answer Correct ? | 5 Yes | 0 No |
how is find out kwh step by step
what happens if dc supply is given to the transformer?
How to calculate incoming cable size for 33KV, 1MVA transformer.
If the rotor pf of a 3 phase induction motor is .866, then what is the phase displacement between stator and rotor magnetic field 1)30,2)120,3)150,4)90 please justify....
What is difference between PLC and SCADA
13 Answers Uflex, Vimal Fire Controls,
why power of fm is weaker than am?
What are the Return ( Monthly / quarterly/ Annual submitted to Electical Inspector for an establishment (Factory in Maharashtra-- Small scale category having seperate HT line of 22KV ) as per Maharashtra Electricity Act
what is the voltage of insulation megger that should be used for measuring the resitance of 66kv equipments.
what is differentila pilot supervision in the incomer control panel in the power station?
1. what is the power factor and whatis his losses 2. what is the working procedure of 51RNB AND 87 relay
why we use 3 phase in our country?..why no 4,5 or 2??
what is use of mccb.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)