why causes the burnt of AC Electrical Motor ?
Answers were Sorted based on User's Feedback
Answer / zahid noor
This question is wrong, it should be what causes ARE
RESPONSIBLE FOR burning of ELECTRICAL motor.
The answer is Motors are burnt due to over heating of
windings, insulation failure,bearing/bush wear & tear, lack
of maintenance like greasing in rotating DE & NDE side ,
under voltage, over voltage & above all due to lack of
protection relays ie if bimetallic over load relays with
proper setting as per running load & Full load current of
motor is provided, motor can not burnt & it will trip on
any abnormal condition.
Is This Answer Correct ? | 74 Yes | 3 No |
Answer / jesus
-Lack of maintenance.
-If the AC power applied is higher than the parameters
already specified for that specific motor.
Is This Answer Correct ? | 31 Yes | 10 No |
Answer / vikash gupta
in case of ac e=-N d(phi)/dt
when in ac motor we applied dc,since in dc, fulx is always
constant,so rate of change of flux w.r.t. time is zero.so
there is no back emf which limits the extremly high
current,that's why due to high current AC Electrical Motor
is burnt.
Is This Answer Correct ? | 26 Yes | 8 No |
Answer / yuvi
Most common reasons
1. Mechanical failure (lubrication, bearings and bushes
etc,.)
2. Insulation failure
Some more reasons I could think of
1. Abuse of the motor (use of ordinary motor like a heavy
duty motor)
2. Improper starters used, frequent restarting of motors.
3. Low quality power supply or wrong type of power source
(DC, 3phase etc.,)
Is This Answer Correct ? | 16 Yes | 2 No |
Answer / guest
over voltage,bearing damage, misalignment to the load
Is This Answer Correct ? | 15 Yes | 4 No |
Answer / bibek
I think motor burns due to lack of maintenance.bearing problem.wrong stator. Wrong O/L relay protection..,,Single phasing..If it is a sleepring motor the another cause is open circuit ROTOR.
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / varun tripathi
1 lack of maintenance. bearings quality,focous on zero-2 motor assembly,
2 check no load amp.& compare with on load amp. it is in range as name
plate .check mech. s/m healthy
3 long servicing renderd of motors. also affect its insulation, rotors strips etc.
4 protection of relay with sute range.& power factor 0.8 = or greater
,supply voltage as need spcification
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dipen dalsaniya
due to the lack of maintenance motor burnt out
over heating,insulation failure
Is This Answer Correct ? | 2 Yes | 2 No |
if dc excitation is used to produce manetic flux in rotating machines then ehy it is not used in transformers.
in delta connection, why motor rotate in high speed compared to star connection?
what is the difference between 3 phase 3wire &3phase 4 wire meter?what is the advantage of 3p3w over 3p4w?
what is v/f control in VFD?
What is the ideal power factor?
use of choke in APFC panels
Is reverse power relay of generator operate due to voltage variation problem? please clearify.
What is Electrical Engineering?
13 Answers L&T, NTPC, Wockhardt,
how we decide scurt (disc) of insulator with respect to kv rating
what is the diffrence between current transformer and voltage trasformer
What is the universal motor?
What happens with squirrel induction machines if the ends of rotor conductors are kept open? Explain