what is cogging and crawling
Answers were Sorted based on User's Feedback
Answer / romesh roy nigam
Cogging - The rotar of squirral cage motar some times
refuse to start at all,particularly when the voltage is low
this when number of rotar teeth becomes equal to numbers of
stator teeth & due to magnatic locking between stator and
rotar teeth.
Crawling - The phenomenon when squirral cage motar some
times showing tendency to run stably at speed as low as one
seventh of its synchronus speed
| Is This Answer Correct ? | 16 Yes | 2 No |
Answer / raul
COGGING : when the stator and rotor poles of a 3-phase
Induction motor r either equal or have an integral
ratio......there is a strong alignment or magnetic locking
b/w the stator n rotor teeths.......so due to this the
motor is unable to start inspite of applying full rated
voltage across the motor........
CRAWLING : it is inability of a 3-phase induction motor to
speed up to desired slip speed and has a tendency to run at
a stable speed of 1/7th of the synchronous speed. this
normally occurs due to the 7th harmonic present in the non-
sinusoidal flux wave.......it can be avoided by using short
chorded windings.......
| Is This Answer Correct ? | 4 Yes | 1 No |
What will be the current if the resistance total in a series circuit doubles?
What is the generating voltage of a power station consided generally?
how we can calcultae the short circuit level for bus bar
0 Answers Jaiprakash, Panorama Apparels,
On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Current: 693A Voltage:294/20KV OLTC Type: T III Y1000 110/c 12193w Max Operation Current: 295A Step Voltage: 550V Arrangement in Tx windings: Y Connection Problem: Damage of Unit 1 Generator Transformer On Load Tap Changer (OLTC) Description of Incident: 9.00 a.m. :- Generator No Load test on excitation system started 10.30 a.m :- Carried out AVR change over test 11.30 a.m :- Preparation for Generator Manual Synchronizing test 12.00 a.m :- Manual Synshronizing test started. Observed incoming generator voltage higher than running voltage. CECR operator operated Generator Transformer OLTC to bring down the incoming generator voltage 12.03 a.m :-Generator Transformer abnormal alarm operated at Gen.Control Desk (CECR) CECR operater at Generator transformer bay informed that the transformer oil splashed out from OLTC. CECR operater informed that he heard explosion inside OLTC. Observed Oil level & Oil Flow alaram operated at Tranformer local annunciator. 12.05 am :- CECR operator 'Open Gen Field Breaker” 12.10 a.m. :- Elec1 team inspected the OLTC and found the OLTC rupture disk was broken and oil spilled at OLTC area. - Elec1 found the OLTC top cover bulging. Do anyone know why and possibility cause happen in this OLTC.
at the time of starting back emf of a motor is zero.so how can it will start to run??
how hazordious area is classified at an oil & gas plant and categorise suitable class of electric equipment in that area like induction motors, LCS, Lighting Fixtures Fluerescent/Flood lights Mercury& sodium lights, J.Bs, Power Cables etc
Hi Recently I got one formula that is Impedence of Xformer = Rated KVA/Root 3 * secondry voltage OF Xformer. Is it Right??????
why power dissipation is due to low frequency?
If OLTC is in manual position there is chance to variation of voltage(Low or High)?
which relay is used for both detection & correction?(there is only one relay)
what is the difference b/w permitivity and permeability
WHY MOSTLY BATTERY VOLTAGE IS IN MULIPLE OF 2 LIKE 2V,4V,8V,16V,18V....
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)